S[SUB](kVA)[/SUB] = I[SUB](A)[/SUB] × V[SUB](V)[/SUB] / 1000

P[SUB](kW)[/SUB] = I[SUB](A)[/SUB] × V[SUB](V)[/SUB] / 1000 x power factor
 
It depends on whether you are answering the topic heading or the original question,

they are not the same.
 

S[SUB](kVA)[/SUB] = I[SUB](A)[/SUB] × V[SUB](V)[/SUB] / 1000

P[SUB](kW)[/SUB] = I[SUB](A)[/SUB] × V[SUB](V)[/SUB] / 1000 x power factor
[/QUOTE

That is the wrong way round isn't it ? KVA should have the power factor element of the equation.


Yes, didnt look at the equations (on phone) hasn't helped at all. But what i wrote still stands. Can't believe this is proving so difficult. If anyone has a link or diagram of the power triangle, it would be a big help.
 
[FONT=Arial, Helvetica, sans-serif]Howto calculate KVA[/FONT]


[FONT=Arial, Helvetica, sans-serif]100ampsx 230 volts / 1000 = [/FONT][FONT=Arial, Helvetica, sans-serif]23kva[/FONT] [FONT=Arial, Helvetica, sans-serif](singlephase)[/FONT]
[FONT=Arial, Helvetica, sans-serif]Thereforea quick ref is 0.23 per line amp.[/FONT]

[FONT=Arial, Helvetica, sans-serif]100ampsx 415 volts x 1.732 / 1000 = [/FONT][FONT=Arial, Helvetica, sans-serif]71.878kva[/FONT] [FONT=Arial, Helvetica, sans-serif](3phase)[/FONT]


[FONT=Arial, Helvetica, sans-serif]Hencea 13.8Kva supply is rounded up to 15Kva for a 60A fuse.[/FONT]
 
Howto calculate KVA


100ampsx 230 volts / 1000 = 23kva(singlephase)
Thereforea quick ref is 0.23 per line amp.

100ampsx 415 volts x 1.732 / 1000 = 71.878kva(3phase)


Hencea 13.8Kva supply is rounded up to 15Kva for a 60A fuse.
What about re-active power and power factor though? We're back to plain Ohms law here. Daz

- - - Updated - - -

Apparent, true and reactive is the power triangle I know...PIV is the PIV triangle :)

Ah, I thought you meant the Ohms law power triangle sorry. Daz
 
Hi All. Thanks to everybody who took time to respond to my post. I didn't think it would cause this much interest so well done everybody.
 