SPUR ok.. Geez those acronyms are starting to sound Americanised
Ok so the existing protective device I have chosen B 60898 16A with a 13A SFCU (switched fused connection unit aka switched spur aka plastic on the wall with neon in it or however you want to refer to it) would that be sufficient. The details off power and length of run are all in the table. Do really need to use a RCBO ?
SFCU is purely part of design. The idea was introduced to us in class. If maintenance work needed to be carried out on either air con unit or heated towel rad. The work could be carried out with out needing to access the DB
You've missed my point, I'm asking why it needs a fuse there?
But you have designed the circuit with the DB in the room you're working in?SFCU is purely part of design. The idea was introduced to us in class. If maintenance work needed to be carried out on either air con unit or heated towel rad. The work could be carried out with out needing to access the DB
Ah ok I know what you mean so it could just be a SCU?
No its not a spur, a spur is an unfused connection to a circuit.
Mentioning a ring circuit (not a ring main) and not knowing what a SFCU is?Yes I gather a “Spur” can be an unfused
Connection to a circuit. For example taking a cable from a ring circuit and spurring to a
Single socket outlet.
I always, along with other sparks called them fused spurs. I’m talking about the single outlet with a fuse carrier. Times have changed it seems
….

Mentioning a ring circuit (not a ring main) and not knowing what a SFCU is?….
Ask for a SFCU in some wholesalers and you might still get a funny look, though..![]()