Hi,

I was doing my r1+r2 tests on a lighting circuit yesterday in a 6 bed house over 3 floors. Approximately 20 points not including switches. Mainly pendants but some light bars etc and almost all LED or low energy halogen type bulbs. Closed circuit r1+r2 values range from 0.88 on ground floor to 3.06 on top floor.

The lights all work ok. I believe I have found one pendant with a discontinuous earth not picked up on a recent EICR done by a 3rd party, which I will return to this week and fix.

However, a couple of pendants were giving me values of over 130 ohms when the switch was open (light off), which I check as part of the polarity test.

Can someone help me understand why these high r1+r2 values might be occurring?

Thanks

Chris

IMG_4494.JPG
 
Ah yes, good question. I should have said.

I have performed a R1+Rn - R2 insulation test and got 130Mohm. Not perfect but acceptable. R1 - R2 has not been done as yet because I don't want to have to remove all the bulbs!
 
Are you confusing readings somewhere? You mention a continuity reading of 130R and an IR reading of 130M. Is it just coincidence you have similar results? (I know they're a factor of a thousand different, bu tyou know what I mean).
 
Are you confusing readings somewhere? You mention a continuity reading of 130R and an IR reading of 130M. Is it just coincidence you have similar results? (I know they're a factor of a thousand different, bu tyou know what I mean).

No its just a coincidence. I've got two pendants its happening on. one is reading around the 130 mark and the other is at 150.
 
Turn the switches on, why have you got them off. You have lost the R1 return at the light with the switch off.
 
Turn the switches on, why have you got them off. You have lost the R1 return at the light with the switch off.

You misunderstand. This is for just one of the two problem pendants. With the switch closed/on I'm getting 2.89ohm but with the switch open I'm getting 150ohm when I would expect to see >2000ohm (open circuit) as I do for all of the other pendants.
 
Hi,

I was doing my r1+r2 tests on a lighting circuit yesterday in a 6 bed house over 3 floors. Approximately 20 points not including switches. Mainly pendants but some light bars etc and almost all LED or low energy halogen type bulbs. Closed circuit r1+r2 values range from 0.88 on ground floor to 3.06 on top floor.

The lights all work ok. I believe I have found one pendant with a discontinuous earth not picked up on a recent EICR done by a 3rd party, which I will return to this week and fix.

However, a couple of pendants were giving me values of over 130 ohms when the switch was open (light off), which I check as part of the polarity test.

Can someone help me understand why these high r1+r2 values might be occurring?

Thanks

Chris

View attachment 37379
Do you mean R1+R2? r1 r2 and rn are for ring finals only
 
Its hard to follow your description of what is your situation but here 's a try

The only thing you are removing when you switch off are the switch live back to the pendant and the switch contacts
If you are now getting 130 ohms where 1000s were expected,it seems to me it can only be via the open switch
Have you measured the switch itself as a separate item
 
Thanks for all the help guys.

An EICR was done but NOT by me. This issue was not raised and neither was the discontinuous earth. The remedials listed were fixed and I have since changed the CU and am testing all the circuits I've moved for my EIC.

There is two way on the hallway lights but not the ones affected. Screenshot below shows my readings.

Thanks again.

Capture.PNG
 
Are you registering voltage between line/earth at the light fitting and is the insulation resistance clear.
 

Reply to Lighting Circuit r1+r2 values. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Have only recently gotten in to testing. Doing an R1+R2 on a lighting circuit but instead of producing a result my tester clicks over and over...
Replies
5
Views
876
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
575
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock