just a quicky if installing class 1 lights on a circuit with no earth (single strand) can i run a earth from a shower etc ?
 
Why not do a rewire,or just pull an earth in to all the lights.Personally i wouldn't.What is the state of the CU:confused:
 
Agree, class 2 or nowt...Same goes for metal-clad type switch-plates, as these need to be plastic on a no-earth lighting circuit.

Yooj
 
they dont want rewire i was originally going to fit class 2 but hard to find class 2 downlights but im with you lot if they dont want rewire they can get someone else to do it
 