Lots of things you can try.
If the main switch is at fault, it will likely respond to being tickled. Very slight movement of the lever or cables will probably cause the flickering to improve or worsen. If it is ever subject to much load, it will probably have got hot due to the increased resistance; look for signs. Check all the MCBs are properly clamped to the busbar, i.e. that the lugs are not the wrong side of the clamps. Again, would be triggered by movement in the board.
If the flickering seems random, i.e. due to a bad connection, yry monitoring the voltage across any suspect part - a few volts, varying with load, across either pole of the main switch would be a clue. If the flickering is suspected of being cyclic, look for sources of line disturbance that are not electrical faults. Large A/C or heat pumps nearby?
Piggyback a 1-way CU feeding a small incandescent lamp, direct from the meter tails with a Henley block. If that flickers too, it's a DNO problem, so you can call them with confidence that nothing is wrong on the customer's side.