im getting proximity to electrical and other services,,, you wouldnt be using he book too older regs, hahah

your right to the on site guide, but this opens up completely when your a man, and what about vold drop..

your pretty dam close tho

ok your pretty much right

Thank you that is all i wanted to know was that i was right or wrong..
 
If this is for an exam, then realy you should have two tests for continuity.
One for continuity of CPCs and bonding conductors.
The other for continuity of RFC conductors.
 
Dead Tests
Continuity of protective conductors (including main and supplementary bonding)
Continuity of Ring Final Circuit conductors
Insulation Resistance
Polarity (can be done while carrying out continuity of cpcs)

Live Tests
External Earth Fault Loop Impedance (Ze)
Prospective Fault Current (PEFC & PSCC)
Earth Fault Loop Impedance (Zs)
Functional Tests
 
and verefication of polarity should be before IR....as polarity is one of the outcomes of continuity (R1 R2 Rn).......
 
Last edited by a moderator:
The onsight guide refers to relevent tests. Under what circumstances wouldnt you have to perfome any of the tests mentioned?
 