Hi everyone, new to this site and just wondering if someone can help. Was called out to see why fluorescent lights were not working, when I put meter across live and earth got 230v, but when I put meter across neutral and earth also got 230v. Would this have anything to do with electronics within light fittings giving me a reversal ?. Would appreciate any advice as it was doing my head in.
 
Sounds like a lost neutral upstream of the light fittings to me.

It's not a PME supply is it???:eek:
 
What do you mean by lost neutral? sorry not long qualified myself and still getting used to some terms.
 
Lenny means that between the light and the CU the neutral has been lost.
effectively the cable is live thru the fitting so that way you are getting a reading down to earth.
 
Would lost neutral be caused by someone playing around with electrics. Guy who owns property used to be a spark and have found signs of tampering. It is a three phase supply coming into a shop. TNS system ( I think)
 
99% sure this is a neutral gone walkies, maybe burnt out in the dis board or loose connection.

Something to be aware of though, if the main neutral has disconnected for whatever reason from the dis board then this becomes alot more hazourdous and you can burn out fittings, computers and all sorts.
 
99% sure this is a neutral gone walkies, maybe burnt out in the dis board or loose connection.

Something to be aware of though, if the main neutral has disconnected for whatever reason from the dis board then this becomes alot more hazourdous and you can burn out fittings, computers and all sorts.

Would the other one percent be the possability that the neutral has been connected into a live connection of a different phase.
The OP didn't tell us what voltage reading he was getting accross live and neutral.....if the reading was around 400 volts it would be a neutral connection to phase 3 or if he was getting 0 volts I would agree that a neutral has become disconected.
 
Apparently lights havent worked for 2 years. Think I will recomend new lighting circuit, probably easier to start again than to fix all the problems that I have come across. Thanks for the advice.
​
 
Guy who owns property used to be a spark and have found signs of tampering. It is a three phase supply coming into a shop.

I dont hold much faith in this guy being a spark, its taking 2 yrs to fix a light and now gets a spark in to fix it.
Sounds like a big can of worms waiting to jump out.Just be careful would be my advice, by the book imo.
 