To answer your questions, if the loads on all phases were roughly the same then their voltages would stay reasonably close to your nominal 230v, and bearing in mind a lot of kit is designed to work within a range of, say, 200-250 volts or even 100-250v no-one would be any the wiser that the voltages on the phases were varying with load. Only when the voltages go outside the tolerances of the appliances (too high or low) would you notice they stop working, or catch fire.
Cheers, its all making sence now, and that does explain how they have been up and running for the past year untill a recent big event at one end of the building, then stuff caught fire.
Thanks very much