Good Afternoon chaps...

Got a few Lutron related questions need a bit of help with please.

Looking at their website which is pretty full on, trying to work out exactly what I need and whether it will work off existing wiring. Dosent make it any easier it being in American - 3way switch and 4way switch ??

Basically the customer likes the look of the 'Diva' range.

On one end we need a 3 gang/2 way dimmer : Switch One ---> to dim 6 x halogen wall lights (1000w dimmer) Switch Two ---> to dim LED strip Switch Three ---> to dim LED strip and the other end just 3 x standard 2 way switches switches ?

The way it's wired at present is feed to switch one end of the 2 way circuit, switched live out the other switch, 3 core between (singles way) ?

Another thing which I need to work out is what back boxes I need, I'm presuming that standard UK ones aren't going to be the right size ?


Another part of this job is having a full blown Lutron Graphik Eye system install. I'm running my 12 different switched circuits back to the controller and then a Lutron/lighting specialist is coming along to do his bit. My question is how do I go about testing this, cant see me getting a Zs - wouldnt fancy risking it anyway ? Suppose all I can do is an R1+R2 and then calculate it..?

Thanks for your help,

Sy
 
Good Afternoon chaps...

Got a few Lutron related questions need a bit of help with please.

Looking at their website which is pretty full on, trying to work out exactly what I need and whether it will work off existing wiring. Dosent make it any easier it being in American - 3way switch and 4way switch ??

Basically the customer likes the look of the 'Diva' range.

On one end we need a 3 gang/2 way dimmer : Switch One ---> to dim 6 x halogen wall lights (1000w dimmer) Switch Two ---> to dim LED strip Switch Three ---> to dim LED strip and the other end just 3 x standard 2 way switches switches ?

The way it's wired at present is feed to switch one end of the 2 way circuit, switched live out the other switch, 3 core between (singles way) ?

Another thing which I need to work out is what back boxes I need, I'm presuming that standard UK ones aren't going to be the right size ?


Another part of this job is having a full blown Lutron Graphik Eye system install. I'm running my 12 different switched circuits back to the controller and then a Lutron/lighting specialist is coming along to do his bit. My question is how do I go about testing this, cant see me getting a Zs - wouldnt fancy risking it anyway ? Suppose all I can do is an R1+R2 and then calculate it..?

Thanks for your help,

Sy

On the testing, you can't test through the dimmer, it's probably a triac that chops the waveform, giving artificially high Zs readings as a result.
Like you say, measure R1+R2 and calculate your Zs from that.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

sythai

Arms
~
Joined
Location
Devon, United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Lutron help please......
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
sythai,
Last reply from
IQ Electrical,
Replies
1
Views
2,303

Advert