A TT install is the very last option you would want to go for!! I would be asking at the very top, how they have calculated 3000 quid to PME a domestic installation!! So what earthing system does have all the other houses have in this street?? For a start, I'd be asking neighbours if i could have a quick look at the service heads... If all are PME or TN-S, then there would be some explaining to do as to why they are quoting 3000 quid, for a job that can be done during the service head up-grade at no extra cost to them whatsoever....
If the DNO themselves got a 0.5 ohm, and actually told you to fit your own earthing means to the sheath, then at the end of the day i would be inclined to do just that with the use a constant force spring earthing clamp. No tools required, absolutely no chance of damaging the lead sheath, and a decent earthing point for the installation....
Absolutely amazes me at times here, how fast some will just bung in a twig for an earth rod, be happy with a 200 ohm Ra and walk away ''actually thinking'' they've done a good job!!!