Maximum demand in all electric flat

Steve T

~
DIY
Hi all,

A family member of mine owns a flat which is all electric with no gas supply. She asked me to give her a hand swapping out her electric shower as it had stopped working, so went to look at it but got me asking a few questions about the installation. List of circuits/appliances is as follows
• 1 x 7.5kw electric shower
• 1 x 6kw electric hob
• 1 x 3kw hot water cylinder
• 1 x 2.5kw oven
• 1 x 2kw panel heater
• 2 x 1kw panel heater
• 1 x 600w panel heater
• 1 x 500w towel rail
• 2 x 32a socket circuits (lightly loaded though kitchen only has space for 2 appliances currently a fridge & washing machine)
• 1 x 6a lighting
• 1 x 6a smokes

After diversity I am getting around 100a, the current main fuse is assumed to be 60a - I have not physically checked this but the holder is actually only rated at 60a so it is probably a fair assumption. Just after your thoughts really as to wether this is actually a problem or not, it must be said the fuse has never blown in the past 3 years shes lived there!

Cheers
 
Worth mentioning, if you look at the characteristic curves for house service fuses, you'll see a 60A fuse won't blow at 100A until nearly an hour has elapsed, and will withstand nearly 90A continuous.
Anything with a thermostat is likely to be cycling on an off once warmed up. Surely lights and smokes won't be 12A, nor the socket circuits more than 2kW for long? Shower say 33A, but briefly!
Applying diversity for hob/oven, assuming no 13A socket, is approx 18A. All the wall heaters/towel rail are approx 18A. Immersion would typically only be on for 2hrs max to heat cylinder from cold, and then short bursts to maintain temp.
I think worst case, you are unlikely to see more than 75A, and that for a short time.
For peace of mind you could put a clamp ammeter on a CU tail, and see what you get.
You might also look at average daily electricity consumption from the bill, in-home display if there is one, or even switch everything on and count the flashes/ watch the meter🤪
Personally, I wouldn't worry!
 
Hi all,

A family member of mine owns a flat which is all electric with no gas supply. She asked me to give her a hand swapping out her electric shower as it had stopped working, so went to look at it but got me asking a few questions about the installation. List of circuits/appliances is as follows
• 1 x 7.5kw electric shower
• 1 x 6kw electric hob
• 1 x 3kw hot water cylinder
• 1 x 2.5kw oven
• 1 x 2kw panel heater
• 2 x 1kw panel heater
• 1 x 600w panel heater
• 1 x 500w towel rail
• 2 x 32a socket circuits (lightly loaded though kitchen only has space for 2 appliances currently a fridge & washing machine)
• 1 x 6a lighting
• 1 x 6a smokes

After diversity I am getting around 100a, the current main fuse is assumed to be 60a - I have not physically checked this but the holder is actually only rated at 60a so it is probably a fair assumption. Just after your thoughts really as to wether this is actually a problem or not, it must be said the fuse has never blown in the past 3 years shes lived there!

Cheers

How did you work out the diversity? there are a couple of ways to do it.

I would suggest whatever way you do it here though it will be over 60A.

Having no gas and being all electric is the problem, 60A is on the lower side for your MD.

It should be free to upgrade to 80A (though being a flat there could be some reasons that could prevent that)

Given the loads I would suggest it is highly likely the main fuse is subject to overload, how often and by how much though is the question that is hard to answer.

Personally if it was me I would just get it upgraded to 80A (should be free) gives you that little bit of wiggle room to prevent repeated overloads over time and the chance the fuse blows at some point due to weakening.

That said it could last years or decades without blowing and response times from the DNO should be fairly quick to restore power, it would be mainly inconvenience and maybe a spoilt dinner if something was cooking!
 
Good advice above.

One possible way of getting a feel for max demand, if you don't have a clamp ammeter already, is to "invest" £10 in (don't laugh) one of these. It has a max hold function, so monitoring the meter or CU tail with cooker and shower on etc could inform the situation. Unfortunately the thing powers itself off after a short while (if it's like the one I have), but does report peak current pretty accurately!
 
Last edited:
Good advice above.

One possible way of getting a feel for max demand, if you don't have a clamp ammeter already, is to "invest" £10 in (don't laugh) one of these. It has a max hold function, so monitoring the meter or CU tail with cooker and shower on etc could inform the situation. Unfortunately the thing powers itself off after a short while (if it's like the one I have), but does report peak current pretty accurately!
Also don't laugh but if you are into Electronics I built a small circuit with a Raspberry Pi Pico W to measure the flashes from the meter, It actually worked really well and hardest part was getting the photo diode to stay in place.

You can hook it up to a mqtt service like home assistant so you can access the data over the web.

Works really well and requires very minimal components, basically a Pi pico W a resistor and a photo diode.

The majority of meters flash once per Watt hour so just a case of counting them.

Here is the original site that explains the concept.


Certainly an option if you can do it because the results are fantastic and it costs very little. A Pico W cost less than a tenner.
 
How did you work out the diversity? there are a couple of ways to do it.
Basically tried used the diversity allowances given in the OSG which would put me at 115A, thought that seems excessive as clearly not all the heaters/water heater/hob/oven/shower will be used at the same time so thought I could easily take 15A off to get to 100A which would obviously be the highest fuse for a standard single phase installation, if thats what was present I would not have thought twice about max demand! If I used the 40% rule of thumb I would get to just under 60a if I assumed only one 32a socket circuit (which seems reasonable for a smallish 2 bed flat), although from what I understand you're not supposed to use the 40% rule when you've got all electric heating?
 
I have got a clamp meter so may well hook that up and ask her to have an occasional look at it. I suppose in real life the highest demand I could imagine would be all the heaters, hot water, and shower and maybe oven on, that in my mind could be a reasonable thing to happen on occasion for example if you've got back from a holiday. That would be well over the 60a although its a fair point that it won't blow unless the overload is large and sustained. Seeing if they'll upgrade to 80A seems very sensible, she was actually wondering about putting in a higher kW electric shower as the 7.5kkW ones are quite weedy but don't think that can be done!
 