Hi all,
A family member of mine owns a flat which is all electric with no gas supply. She asked me to give her a hand swapping out her electric shower as it had stopped working, so went to look at it but got me asking a few questions about the installation. List of circuits/appliances is as follows
• 1 x 7.5kw electric shower
• 1 x 6kw electric hob
• 1 x 3kw hot water cylinder
• 1 x 2.5kw oven
• 1 x 2kw panel heater
• 2 x 1kw panel heater
• 1 x 600w panel heater
• 1 x 500w towel rail
• 2 x 32a socket circuits (lightly loaded though kitchen only has space for 2 appliances currently a fridge & washing machine)
• 1 x 6a lighting
• 1 x 6a smokes
After diversity I am getting around 100a, the current main fuse is assumed to be 60a - I have not physically checked this but the holder is actually only rated at 60a so it is probably a fair assumption. Just after your thoughts really as to wether this is actually a problem or not, it must be said the fuse has never blown in the past 3 years shes lived there!
Cheers
A family member of mine owns a flat which is all electric with no gas supply. She asked me to give her a hand swapping out her electric shower as it had stopped working, so went to look at it but got me asking a few questions about the installation. List of circuits/appliances is as follows
• 1 x 7.5kw electric shower
• 1 x 6kw electric hob
• 1 x 3kw hot water cylinder
• 1 x 2.5kw oven
• 1 x 2kw panel heater
• 2 x 1kw panel heater
• 1 x 600w panel heater
• 1 x 500w towel rail
• 2 x 32a socket circuits (lightly loaded though kitchen only has space for 2 appliances currently a fridge & washing machine)
• 1 x 6a lighting
• 1 x 6a smokes
After diversity I am getting around 100a, the current main fuse is assumed to be 60a - I have not physically checked this but the holder is actually only rated at 60a so it is probably a fair assumption. Just after your thoughts really as to wether this is actually a problem or not, it must be said the fuse has never blown in the past 3 years shes lived there!
Cheers