telectrix ~ Mentor Arms Nov 24, 2013 #16 stick a 80A isolator/MCB after the DNO fuse/meter. that way any overload will mean a simple reset of the breaker and protect the 100A fuse.
stick a 80A isolator/MCB after the DNO fuse/meter. that way any overload will mean a simple reset of the breaker and protect the 100A fuse.
G Guest55 Nov 24, 2013 #17 telectrix said: stick a 80A isolator/MCB after the DNO fuse/meter. that way any overload will mean a simple reset of the breaker and protect the 100A fuse. Click to expand... 80a fuse discriminate with a 100a fuse ? not in a million years.
telectrix said: stick a 80A isolator/MCB after the DNO fuse/meter. that way any overload will mean a simple reset of the breaker and protect the 100A fuse. Click to expand... 80a fuse discriminate with a 100a fuse ? not in a million years.
telectrix ~ Mentor Arms Nov 24, 2013 #18 biff55 said: 80a fuse discriminate with a 100a fuse ? not in a million years. Click to expand... what i said was a 80A MCB. 100/1 should trip before a 1361 blows.
biff55 said: 80a fuse discriminate with a 100a fuse ? not in a million years. Click to expand... what i said was a 80A MCB. 100/1 should trip before a 1361 blows.