The point of an RFC is to supply a diverse and distributed load, which allows the use of cable and accessories of lower rating than the OCPD. A single heavy load at one point could encourage overloading of one leg, but one could avoid cable overload by using a larger cable as suggested by the OP. 4mm² T+E Method 3 is OK on a 32A, so would withstand the whole 7.4kW load in one place on the ring. One would have to ensure that any connectors and accessories through which the circuit passes are OK for 32A as well.
However, returning to the original intent of the RFC, it might not be the most suitable option as all the cable then needs to be uprated instead of one radial to the large fixed load. Also, as a non-standard implementation of an otherwise standard circuit, in a domestic situation without technical oversight, inappropriate modifications could reasonably be foreseen (such as extending with 2.5mm²) and therefore the heavy point loads still inadvisable on a 32A RFC of any cable size.