Table 41.3 in the regs states Maximum Zs for type B breaker 60898 is 1.44 ohms, the domestic electrical installation cert asks what is the Max Zs permitted. Do you insert 1.44 or the lower figure that is mentioned in the on site guide after fault temprature etc has been allowed for. I've been inserting what the table tells me 1.44ohms
 
Agreed. Maximum Zs according to 7671.

Your reading should be within 80% of this value at normal operating temp.
 
Just to chuck a spanner in. If it's a domestic situation the max Zs is meaningless if it is under 1667 ohms because the 30mA RCD will kick in 1st


Devils Advocate
 
An RCD can be used where disconnection times CANNOT be met.

Its not a get out clause.:)
 
An RCD can be used where disconnection times CANNOT be met.

Its not a get out clause.:)


Never said it was.......... But what i am saying is....... Prior to the 17th if like you say disconnection times could not be met.

We should fit a 30mA RCD

Now with the 17th in a domestic situation we fit 30mA RCD as standard, so technically it shouldn't matter as long as it's below 1667 ohms.

I'm just playing Devils Advocate.
 
Never said it was.......... But what i am saying is....... Prior to the 17th if like you say disconnection times could not be met.

We should fit a 30mA RCD

Now with the 17th in a domestic situation we fit 30mA RCD as standard, so technically it shouldn't matter as long as it's below 1667 ohms.

I'm just playing Devils Advocate.

Fair do's! :D
 
Would it not be correct to state that the new requirement for rcds in b.s. 7671 2008 is for Basic protection against shock ,by careless users .Granted ,the rcd is also providing a degree of Fault protection and would allow for a theoretical allowable Zs of 1667 ohms.....however the circuit should have been designed with the Protective device providing the primary function of Basic protection, and as such it is the c.b value of max Zs and not the rcd value of max Zs which should be entered into the data box.


Regards..............spark1
 
Would it not be correct to state that the new requirement for rcds in b.s. 7671 2008 is for Basic protection against shock ,by careless users .Granted ,the rcd is also providing a degree of Fault protection and would allow for a theoretical allowable Zs of 1667 ohms.....however the circuit should have been designed with the Protective device providing the primary function of Basic protection, and as such it is the c.b value of max Zs and not the rcd value of max Zs which should be entered into the data box.


Regards..............spark1

Yes you are correct...
 
Cheers Jason...........I meant to insert an image reply but not sure how to..........any help available ?

Cheers Jason ! i intended to reply with an inserted image ,but being new to posting here i am not sure how to...........any tips ?

oops double posted also........sorry !
 
Last edited by a moderator:
Can't believe what I'm reading here, chaps

A 30 mA Rcd is additional protection and only reacts to an Earth Fault

You can't just bang a 30 mA Rcd in and forget about maximum Zs

What about Overload or Short Circuit??

1667 is max Zs for a TT system and even then you wouldn't leave it
anywhere near that high because you wouldn't meet you circuit breaker
disconnection times!

Come on!
 
Can't believe what I'm reading here, chaps

A 30 mA Rcd is additional protection and only reacts to an Earth Fault

You can't just bang a 30 mA Rcd in and forget about maximum Zs

What about Overload or Short Circuit??

1667 is max Zs for a TT system and even then you wouldn't leave it
anywhere near that high because you wouldn't meet you circuit breaker
disconnection times!

Come on!

I agree 411.5.3 states 1667 is the max impedance to ensure rcd opperation note 2 asks for an impedance as low as possible and not exceding 200 ohms
 
Just re-read my post and kind of confused myself.

What I think I'm trying to say is this

You should try get your Zs as low as possible (certainly within the limits

given for the breaker that your using), so that the breaker will trip under

any fault condition, thereby protecting the circuit.

A 30mA Rcd is additional protection against electric shock
and will therefore trip at 5I in 0.04 seconds -
but not all circuits are suited to Rcd protection, are they,
so you have to get the Zs to the limits stated

I think Ive got it right now

Cheers

Wayne
 
wayne & wotsit............agreed ! ...no argument there.

As I said.........but put another way !


Regards........spark1...........
 
Hi Guys, according to the NIC the 1667 value should be entered into the maximum Zs box, not the values in table 41.3. So if your filling in NIC certs i would use 1667 ohms. I got pulled for NOT using 1667 on my last inspection. I;m not saying it's right just sayimg what the NIC want to see in that box.
 
I've always used the values from the appropriate table never just 1667 for all, as if the circuit is without RCD, anything over these values doesn't comply and the device wont operate.

Been an NIC contractor for a few years now, never said anything like that to me.
 
I totally agree lenny, up to my last visit i have never used 1667 as a maximum value, just letting you know what tis gut said. His name is Warren Clarke. If any one else has come across him on an assessment i would be interested to know what he said to them.
 
Got to be honest I'm becoming more and more disillusioned with the NIC, one inspector says one thing and another says another. They're getting a lot of bad press lately and it seems they'll take your nan on board as long as she can breathe!!!
 
Same here, the ONLY reason i'm still with them is that i do a lot of kitchen work for the John Lewis Partnership and they insist on NIC enrollment. If it wasn't for them i'd be off elsewhere!
 
As far as im concerned the ONLY time 1667 Mx Zs is entered on my EIC is if its a TT install.

The NIC seem to have their own rules, and its not only about this.
 
You can't just bang a 30 mA Rcd in and forget about maximum Zs

Couldn't agree more Wayne, a lot of people seem to think that this is the answer, but not in my book. Also on a new installation I have never failed to meet the max Zs values, if consideration is given at the design stage then there is no reason not to meet it.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

EddieB

Arms
-
Joined

Thread Information

Title
maximum Zs
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Thread Tags

Advert

Thread statistics

Created
EddieB,
Last reply from
Guest123,
Replies
23
Views
7,409

Advert

Back
Top