Engineer54
I don't see the big deal. In a domestic situation the earth bar of the CU can act as the MET as it is usually provided with a couple of bonding terminals as well as an earth. If you struggle to get a 16mm earth and several bonds into an earth bar THEN it would be appropriate to install a separate MET. Neither option is right or wrong - it depends on the application.
There is nothing wrong in using the CU's earth bar as the MET, but if i were you, i'd take notice of what's being told to you here, by the more experienced electricians. For the sake of a couple of quid, that external MET earth block is far more versitile than cramming 16 and 10mm cables in to a domestic CU.