Just needing to upgrade a mk 5780s RCD to a type A so I can fit a car charger. Does anyone know if a MK Sentry RCD will fit, or have the dimensions changed?

Happy Friday

Jon
 
Seem a pretty good match. The bottom terminals are spot on, in terms of where the bus bar is pressed against. The top terminals are 2-3mm further back, but that's where the tri-rated cable goes so should be ok.

Resize_20230310_082358_8477.jpg


Resize_20230310_082358_8871.jpg


Resize_20230310_082359_9196.jpg


Resize_20230310_082359_9506.jpg


In the first picture (of the bottom terminals), it looks like the one on the right (Type A) is very slightly lower, but this is just the poor lighting and the difference in terminal sizes that makes it look that way.
 
That's awesome, thank you very much! Looks close enough!

Have a great weekend 😊
You just dropped lucky... I'm replacing one on Tuesday next week so have the new one in, and I replaced another one a few weeks ago and kept the old one as an emergency spare. If you'd asked before yesterday, or after Tuesday, I wouldn't have been able to send photos!
 
  • Like
Reactions: Jim_e_Jib
A charge point should not be sharing an RCD. It needs to be dedicated.
 
  • Like
Reactions: DPG
You just dropped lucky... I'm replacing one on Tuesday next week so have the new one in, and I replaced another one a few weeks ago and kept the old one as an emergency spare. If you'd asked before yesterday, or after Tuesday, I wouldn't have been able to send photos!
Ha ha, thanks again!!
 
I would be concerned that the new MK stuff (with the H prefix) may not be suitable for the older MK Sentry units- this from the end of the current MK Sentry catalouge
-------------------------------------
Made in China The MK Trademark is used under license from Novar ED&S Limited Novar ED&S Limited makes no representations or warranties with respect to these products. This product is manufactured by CircPro (UK) Limited, a division of Yihua
 
I would be concerned that the new MK stuff (with the H prefix) may not be suitable for the older MK Sentry units- this from the end of the current MK Sentry catalouge
-------------------------------------
Made in China The MK Trademark is used under license from Novar ED&S Limited Novar ED&S Limited makes no representations or warranties with respect to these products. This product is manufactured by CircPro (UK) Limited, a division of Yihua
Why do you think this makes them potentially unsuitable? They have been clearly designed to be a 'continuity' MK Sentry equivalent at least in looks and branding etc and there is nothing to suggest they are not compatible in MI. Dimensions wise as above. I have replaced a couple of DP RCDs as suggested above with no issues. I did recently replace a Sentry MCB with a current Type A RCBO and whilst that fitted pretty well and the busbar lined up perfectly, the busbar finger was a little long for the depth of the terminal so required a small lick of the file. A crime has been commited I realise that and will probably never sleep soundly again.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
MK 5780s replacement
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
jpelectrical,
Last reply from
grumpyjohn01,
Replies
7
Views
3,502

Advert