I’m not sure of MK, but every other make of SPD has had an mcb before it in the boards.
The new Proteus from CEF are making a big deal that their SPDs have an internal fuse, which frees up a way in the board.

It might be interesting to see if other brands offering the same kA surge protection have the same size mcb up front (from memory, 32A)
FuseBox SPD1MT2 are direct to busbar with no mcb i used one recently.



So does

The Wylex NMT2SPD3W/1 a single module Type 2 Surge Protection device that has been designed for use in Wylex consumer units. It is easy to install, connecting directly to the busbar in the same way as an RCBO
 
Last edited:
But what rating?
Ideally I would try to rate the MCB as high as I could, but would still allow selectivity with the main cutout fuse should the SPD fail short circuit. Alternatively, I'd have thought a 32A MCB would be fine, which seems to be the standard for SPDs in CU's.

Out of interest, what's the earthing arrangement for this installation?
 
Brother Blue pointed out that there is a reference to a requirement for external protection - but I have to say it is not easy to spot.
I'd say it is as easy to spot as all of the other characteristics on that data sheet.
Bother Blue, I do take your point that the maximum should be 125A, so, again, not definitive.
How is that not definitive? It is a definite maximum rating, you work within that and establish what is appropriate for your installation. Pretty much every installation is going to be different in it's characteristics and requirements.


Are you having the same difficulty selecting a cable size because the manufacturer only tells you the maximum capacity of the terminals?
 
Thanks Avo Mk8, that was an interesting vid, it's partly a sales pitch, but does have relevant insights. Thanks also to littlespark, mickegh and mainline for your suggestions of alternative brands to consider. Pretty Mouth, the earthing arrangement is TT and your thinking that 32A should be about right corresponds with the various retailers I've asked about this; they've suggested the same but without any certainty. On balance I might try for the Fusebox single module or the Wylex one. Thanks to all.
 
Thanks Avo Mk8, that was an interesting vid, it's partly a sales pitch, but does have relevant insights. Thanks also to littlespark, mickegh and mainline for your suggestions of alternative brands to consider. Pretty Mouth, the earthing arrangement is TT and your thinking that 32A should be about right corresponds with the various retailers I've asked about this; they've suggested the same but without any certainty. On balance I might try for the Fusebox single module or the Wylex one. Thanks to all.
Ah, a TT earthing arrangement, there is something else we also need to consider here.

Should the SPD failed closed circuit between L and E, the low fault current that would flow in a TT system isn't going to trip the MCB. The earthing system would go live indefinitely.

To the best of my knowledge, there are two ways to overcome this:

1. Fit the SPD downstream of an RCD (as well as the MCB). Not ideal though, as transients can cause it to trip, though a time delayed RCD shouldn't suffer this AFAIK.

2. Just use the MCB, but use an SPD that uses connection type 2 (note 'connection type' is a different thing to 'type of SPD'). CT2 is arranged so you have line-SPD-neutral-SPD-earth. If the SPD fails closed circuit between L and E, then L shorts to N, tripping the MCB.
 
If you buy an MK populated Consumer Unit the SPD is connected directly to the Main Switch. Does this not indicate that this is how the Manufacturer intends it to be used, i.e. no MCB.
 
If you buy an MK populated Consumer Unit the SPD is connected directly to the Main Switch. Does this not indicate that this is how the Manufacturer intends it to be used, i.e. no MCB.
Yes for that SPD .. Is it the same model as above query

I just Googled 6820s MK and the first link is TLC with the data sheet there on the page 😁
 