Hi guys, I want to fit an MK spd, one of their 2-module type 2 H6820s and I can't find anywhere what kind of overcurrent protection to fit with it. Looking at the data sheets, they mention overcurrent protection being 50 kA - but that's not what I mean; what (if any) mcb should I fit with it? One of you super-experienced sparks must know... Thanks for any help!
 
Looking at consumer units online some are connected through a 32A mcb some are not.
 
Thanks for that, Brother Blue. I looked on the data sheet on assets.cef.co.uk but didn't see that...?

It's in the grey box on the right hand side of that data sheet.
Max mains-side overcurrent protection: 125AgG

125A is the current rating and gG denotes a general service BS88 fuse.
 
Thanks Avo Mk8 and Brother Blue. There still doesn't seem to be a definitive answer, though. MK have always made a great product, but they're a bit rubbish with their after sales info.
 
As I understand it, SPDs can fail closed-circuit. If it does, then the upstream protective device should operate. Often this is an MCB, but some SPDs have their own internal protection (Hager SPDs apparently do), in which case you can omit the MCB. If the MK SPD doesn't have internal protection, and the first upstream device is the main fuse, then a failure will take out the main fuse, which isn't ideal. Might be worth you sending MK a quick email to clarify this.
 
Thanks Avo Mk8 and Brother Blue. There still doesn't seem to be a definitive answer, though. MK have always made a great product, but they're a bit rubbish with their after sales info.

The answer above is pretty definitive, an OCPD with a rating up to a maximum of a 125A BS88 fuse.

So you could use a fuse, MCB or MCCB of a rating below or equal to that.
 
I did wonder if it's ideal to have a separate protective device upstream on a domestic SPD

There is theoretically some risk of it being cut out
 
Thanks to all - there's a good dialogue going on here! Much appreciated! Pretty Mouth, I did try emailing MK - no reply. They seem to have been bought up by Novar ED&S ltd, so my query dead-ended. mickegh, it isn't obvious from the casing or from the data sheet if there is an internal mcb of some sort; Brother Blue pointed out that there is a reference to a requirement for external protection - but I have to say it is not easy to spot. Compnies like Surge Protection Devices ltd are quite willing to tell you what is required, but MK have not. Bother Blue, I do take your point that the maximum should be 125A, so, again, not definitive. Also, a company making a relatively modern device such as an spd shouldn't be going back in time by recommending a BS-88 fuse for overcurrent protection. So, yes, and mcb or an mccb would be more appropriate. But what rating? No-one seems to know for sure.
 
I’m not sure of MK, but every other make of SPD has had an mcb before it in the boards.
The new Proteus from CEF are making a big deal that their SPDs have an internal fuse, which frees up a way in the board.

It might be interesting to see if other brands offering the same kA surge protection have the same size mcb up front (from memory, 32A)
 