Thanks to all - there's a good dialogue going on here! Much appreciated! Pretty Mouth, I did try emailing MK - no reply. They seem to have been bought up by Novar ED&S ltd, so my query dead-ended. mickegh, it isn't obvious from the casing or from the data sheet if there is an internal mcb of some sort; Brother Blue pointed out that there is a reference to a requirement for external protection - but I have to say it is not easy to spot. Compnies like Surge Protection Devices ltd are quite willing to tell you what is required, but MK have not. Bother Blue, I do take your point that the maximum should be 125A, so, again, not definitive. Also, a company making a relatively modern device such as an spd shouldn't be going back in time by recommending a BS-88 fuse for overcurrent protection. So, yes, and mcb or an mccb would be more appropriate. But what rating? No-one seems to know for sure.