most common causes for rcds to trip when main DB upgraded ?

appliances , borrowed neutral , fault elements ??

any more less obvious ??
 
Cumulative leakage.

Do you have a problem?

EDIT: Obviously this isn't real as no one installs boards with single RCD's any more DO THEY?
 
Last edited by a moderator:
is this a round about way of saying you have a fault , cant work it out , and now need our help ?
:-)
 
any more less obvious ??

1. Appliances with high protective conductor currents by design e.g. mains filtering.

2. Capacitive discharge currents? Dunno about this one but always wondered about it as a theory.

3. Someone testing Zs on the wrong setting, e.g. the pixies that live in the electrified garden shed.

4. Someone getting an electric shock.
 
I seem to keep finding small mk sockets with an odd design where the earth is in the middle. So again a N-E fault. Normally found in the back of a cupboard with a fridge attached too.
 