timo1

Hi. Just wanted to double check to see if my interpretation of the regs is ok. I'm adding a 10mm bond to gas services at the request of a landlord for part of a gas safety certificate. The property is an upstairs flat, gas meter is at ground level.

The gas pipe goes up the wall and into the kitchen. I read the regs as bond to be 600mm at point of entry into house, which is relatively easy to take back to the cu. I have a feeling that the gas man may insist on the bond being made at the meter and want to make sure I'm on solid ground if I disagree. Does anyone disagree with me?

ultomately I could bond at the meter but will be a bit of a pickle, and I'm hoping I can avoid drilling an external hole into flat.
 
where it enters the flat. as you correctly say, within 600mm of point of enrty.
 
Aye, the only reason you'd put it anywhere else is if it was inpracticable to get it within 600mm.

However in your case, 600mm is easy so therefore it has to go there.
 
There's some flats near me, 6 gas meters outside at street level and pipes going up the wall to each flat.
Plus, great long lengths of 10 mill GY clamped at the meters, flapping around in wind.
 
I managed to get a clamp on just as it comes in underneath the kitchen units. had to make a nice "inspection" hole inside one of the units but continuity was excellent back to the meter so what I thought was going to be a pain was a relatively quick job. Flat is a 1960s build and I also learned that gas bonding was not required until 1966 isnt that interesting? Bet you wish you were sat next to me at a wedding...
 
There's some flats near me, 6 gas meters outside at street level and pipes going up the wall to each flat.
Plus, great long lengths of 10 mill GY clamped at the meters, flapping around in wind.

sounds like a job i was looking at recently. BG done it when they fitted a new boiler. 10mm gn/y just thown across the outside of the house to the gas meter. pathetic.
 