Ok, had far too much to drink last night and wish I'd done this estimate yesterday but didn't and need a sanity check.

New dual fuel cooker being installed (gas ovens) and electric hob

This is the electrical spec

Power ratings - hob 1 x 1kW, 2 x 1.7 kW, 1 x 3.0 kW, 1 x 3.5 kW, 2 x 1.1kW

Total hob rating @ 230v 13.25 kW

Maximum electrical load @ 230v 11.8 kW = 51A

So we all know it won't draw 51 amps and looking at the run I'd prefer to install a 6mm cable which would be good for approx 38A


Help!
 
Never assume as are AN electrician and you dont know characteristics or distance of cooker run




- - WHAT GOOD IS POSSIBLY ????

So you tell me what difference will it make then, the quoted KW remains the Same??


6mm on a 32A MCB is good for cooker loads up to 15KW. You would have to go some, for distance and cable factors, to change this typical circuit compliance!! Literary Millions of homes in the UK will have exactly the same circuit make-up.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
My head hurts - cooker cable calc
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
Octopus,
Last reply from
Geoffsd,
Replies
28
Views
9,276

Advert

Back
Top