Ok, had far too much to drink last night and wish I'd done this estimate yesterday but didn't and need a sanity check.
New dual fuel cooker being installed (gas ovens) and electric hob
This is the electrical spec
Power ratings - hob 1 x 1kW, 2 x 1.7 kW, 1 x 3.0 kW, 1 x 3.5 kW, 2 x 1.1kW
Total hob rating @ 230v 13.25 kW
Maximum electrical load @ 230v 11.8 kW = 51A
So we all know it won't draw 51 amps and looking at the run I'd prefer to install a 6mm cable which would be good for approx 38A
Help!