leep82

~
Arms
recently been to look at a job where the customer wanted LED downlights installed in there bathroom. Once up in the loft i realised the job wouldnt be as easy as id hoped for ( are they ever ). The first thing i noticed was very old rubber cable (live/neutral but no c.p.c). I wasnt initailly concerned as i thought this may not be in use, especially as additions/alterations had been carried out using T+E however i was soon to be found wrong. It turned out that the old cable was in fact the upstairs lighting feed. The house had recently been decorated with fancy light fittings and switches so the look on the homeowners face and her line of ' but its been fine for years' was no surprise when i tried to tell her the dangers that could exist, and that the only viable solution was to rewire the circuit. Now luckily there is a redundant T+E shower feed in the loft that has been made safe in the DB. I plan on using this as a new feed, then with a JB in the loft rewire using existing switch drops in new T+E. My problem/issue is at the mains, where i have a PME supply, water and gas bonds are fine. The DB itself is a split load Wylex board and there are no spare ways on the RCD protected side for me to use, i was thinking of using an RCBO to get me round this,but when in the board i noticed a circuit that is supplying socket outlets that was also on the unprotected side. I will obviously carry out an initial verification on my new circuit, and should my results be satisfactory is that as far as i need go? i was wondering would i be best to advise the customer on DB change or additional work to sort the sockets issue. Or as i havnt actually worked on that circuit do i not need take responsibility and just maybe make a note/recommendation on my test results?
 
As long as you havent done any work on that circuit, you dont have to rectify it. But note it down on your eic and tell the customer, of your concerns.

it might be worth seeing if shes willing to fork out the extra to put it on an rcbo instead of an mcb.
 
Cheers Tim, I thought as much, frustrates me why people don't have there electrics tested as and when they should, always seem to get there house straight before considering any electrical work and then when you tell them the bad news, chasing to be done, floor boards up etc they look as If they could kill you. Looking at the state of the house I'd be very surprised if once a RCBO was fitted there wasn't problems with nuisance tripping or somthing, I'll point it out to them and then the balls in there court
 
If it was wired to the 16th edition it wasn't mandatory for all sockets to be Rcd protected, only those where it was likely they could be used for outside use.
 
That all sounds so familiar....

My take on it is you are responsible for what you do.

That is the circuits you work on.

But you will have a duty of care to report any deficiencies you find, such as rubber cable with no cpc. and how to get an RCBO into the equation for the lighting circuit in the bathroom, any sockets that might be reasonably expected to feed loads outside.

When i come across this scenario I point the client towards all the ESC information so that they know I'm not trying to pull a fast one.
 
Cheers Tim, I thought as much, frustrates me why people don't have there electrics tested as and when they should, always seem to get there house straight before considering any electrical work and then when you tell them the bad news, chasing to be done, floor boards up etc they look as If they could kill you. Looking at the state of the house I'd be very surprised if once a RCBO was fitted there wasn't problems with nuisance tripping or somthing, I'll point it out to them and then the balls in there court

If they need a reason as to why its important to replace the old rubber cable, show them this pic, my mate just moved in and asked me to check the electrics, i ended up rewiring the house.

e3umupu8.jpg
 
Been there, done that so many times. The prevailing attitude of many customers is that if it works and looks nice then you must be trying to rip them off. Makes me cry sometimes, especially when I've had to walk away from a job knowing that there is potential danger lurking at someone's house.
 
When I was at the Elex show I picked a few properly printed copies of the ESC homeowner info sheets. Stuff like "what do you need an RCD", "what is part P", "why check earthing and bonding" etc. I am not a big fan of the wording of some of them but the great advantage is that they look official so it is not just me trying to scare my customers into spending money.
I think you can get them by post if you check the esc website.

Apologies for the topic drift, I agree with the others, do what you can, make sure what you did was safe and put any concerns on the rest in writing to the customer. If anything is actually dangerous (like that picture from Tim) then issue a nice red danger notice :)
 
Thanks for that brman, ill print some of those off. As you said it looks better to have an official leaflet so it doesnt look like your mAking stuff up to get more work
 