Hi guys i need some advice and i would appreciate your feedback.

i have just extended an existing circuit by putting in 2 way switching in a house in london, all was going well until i came to test the installation, and i have discovered that i can't get an r1+r2 reading from the metal (old R80 style) light fittings in the 1st floor landing ceiling. all the other lights and switches are fine on the circuit!?! i'm thinking there is a j/b in the ceiling somewhere that i cant access that has the cpc disconnected.

what would you guys do in this situation? could i change the metal lights to plastic, or would you state the problem on the cert?

thanks for reading my problem and thanks in advance for any advice.
 
Im with Murdoch and Kate on this too. Change the offending fitting to plastic/class 2, slap a warning label on the CCU advising not to fit 'metal' and note everything you've done on the cert!
 
You have not wired the lights so the options are...
1.Sort it with the clients agreement,either by providing an earth or fitting class II lights.
2.If the client wont agree to remedial work note it on the minor works cert you will be providing for the work you have carried out,and recommend that it is rectified,you are not obliged to rectify this just because you have installed a 2w switch addition.Make sure the extent of your work is absolutely clear on the cert.
 
thanks guys, i will recommend fitting a class 2 light fitting to the customer tomorrow, and will put a yellow sticker on the ccu, now i've just got to find a nice looking plastic light big enough to cover a 5" hole that the R80 will leave behind!!!

i appreciate the quick responses
 
thanks guys, i will recommend fitting a class 2 light fitting to the customer tomorrow, and will put a yellow sticker on the ccu, now i've just got to find a nice looking plastic light big enough to cover a 5" hole that the R80 will leave behind!!!

i appreciate the quick responses

Doesn't have to be plastic. Plenty of downlights with metal frames and bezels are class 2. Adaptor plates are available for some to cover existing large holes.

Actually, just a thought, are the old fittings class 2 anyway, despite being metal?
 