Its not no but fault finding is not my speciality i spent a vast majority of my apprenticeship building switchboards. just some clarification on what the formula wll tell me in regards to my issue??
 
Ive never come across voltages when a device has been switched off? Apart from of course induced voltage which i personally dont think this is considering the length pf the run? I may be completely wrong
 
you could try fitting a snubber across the switch L and N to the affected light.
 
Sounds like a fault in the circuit to me, 70 volts? hmm, transformers anywhere by any chance? LV Bathroom fan connected to same switch wire?
 
99% it is inductance.
Use an analogue meter to test the voltage, it will read nothing.
Do a loop test, it will read nothing.
I've had it a number of times in the past, it is always cheap CFL lamps that have been swapped in for a filament lamp.
It will have done it for years beforehand, but now the internal electrics of the lamp you have in are causing the occasional flickering, whereas a filament element will just heat up ever so slightly, and not be visible.
 