Monchichak

Morning!

Trying to decide on the most appropriate/cost effective distribution board?

Supply: 3 phase 400A
Circuits:
7 x single phase (16 - 60A)
1 x 3 phase (80A)
+ 6 single for future proofing

Setup: Main supply comes into pump house where fuse, meter & distribution board will be located - each outgoing way feeds a different workshop/unit on the farm (requires 300mA RCD - Regs 705.411.1 iii).

Are there any particular makes/models to go for/steer clear of?

I've got little experience in anything over 100A so all your advice is much appreciated.
 
We use Schneider..
 
IS THAT 400a PER PHASE, OR TOTAL?
 
Morning!

Trying to decide on the most appropriate/cost effective distribution board?

Supply: 3 phase 400A
Circuits:
7 x single phase (16 - 60A)
1 x 3 phase (80A)
+ 6 single for future proofing

Setup: Main supply comes into pump house where fuse, meter & distribution board will be located - each outgoing way feeds a different workshop/unit on the farm (requires 300mA RCD - Regs 705.411.1 iii).

Are there any particular makes/models to go for/steer clear of?

I've got little experience in anything over 100A so all your advice is much appreciated.

You will be limited in what you can fit if you want to install a 80A MCB.

If it is 400A it would need to be an MCCB panel board to be rated to 400A.
 
If you have 400A coming in then maybe something like this. See if it's suitable for you.
 
Schneider Powerpact for me too. Quite pricey but can't fault 'em.

Chint make me squint....but I've never used their equivalent.
 
Thanks for your replies, the Powerpact looks like a strong contender.

It's 200A per phase supply but in the supply upgrade requirements it states the tails & main switch must be sized for the 400A cutouts.

Perhaps it would be cheaper to fuse the supply down to 200A?
 
Thanks for your replies, the Powerpact looks like a strong contender.

It's 200A per phase supply but in the supply upgrade requirements it states the tails & main switch must be sized for the 400A cutouts.

Perhaps it would be cheaper to fuse the supply down to 200A?

What are you responsible for? Just the CU and the outgoing circuits?
 
Thanks for your replies, the Powerpact looks like a strong contender.

It's 200A per phase supply but in the supply upgrade requirements it states the tails & main switch must be sized for the 400A cutouts.

Perhaps it would be cheaper to fuse the supply down to 200A?

Maybe seek clarification on the requirements. That makes no sense to me.
 
You have only worked on 100A supplies do you have the tools for terminating 240.0mm+ size conductors.
 
I always like melin gerin, with a 400 amp DB you would also need a looping in box under the board to help with the cable in due to the size of the cables, However Schnieder is also good kit.
 