You're right in thinking that a well trained monkey can wire a house (Christ I've been doing it for years :) ) but if you think that this course has taught you all you need to know you're very very wrong mate.
The government has not got a clue when it comes to this, they came out with the regulation as a knee jerk reaction to a death and to make sure we're all good boys and girls and pay our taxes. The schemes are only interested in one thing, your money. You'll see in time that there are some absolutely appaling installations out there which have been done by fully badged up scheme members.
Just as a little example, you have rewired a property on a TT, it's been raining for a few days so the ground is wet. You measure your Ra and it is 198 ohms, obviously lower than the maximum allowed in 7671. What do you do?
Not all of the people who come away from the Electrical Trainee courses are dangerous. Some, like you appear to, know their limits and realise how much they don't know then go and make sure they do know it for next time.
 
You're right in thinking that a well trained monkey can wire a house (Christ I've been doing it for years :) ) but if you think that this course has taught you all you need to know you're very very wrong mate.
The government has not got a clue when it comes to this, they came out with the regulation as a knee jerk reaction to a death and to make sure we're all good boys and girls and pay our taxes. The schemes are only interested in one thing, your money. You'll see in time that there are some absolutely appaling installations out there which have been done by fully badged up scheme members.
Just as a little example, you have rewired a property on a TT, it's been raining for a few days so the ground is wet. You measure your Ra and it is 198 ohms, obviously lower than the maximum allowed in 7671. What do you do?
Not all of the people who come away from the Electrical Trainee courses are dangerous. Some, like you appear to, know their limits and realise how much they don't know then go and make sure they do know it for next time.
pray for more rain or do a rain dance
 
OK so 198 is below the allowed 200, but it will increase as the ground dry's up right?, so that 198 will almost certainly take the Ra/Ze to over 200. (whats the difference between Ra/Ze btw, are these terms interchangable?) Could you provide a 2nd parallel path for the rod maybe? I'm not sure.
 
I can fly a 747 in a flight simulator because I followed the instructions, but does that mean and airline will let me loose with a $150 Million plane and 400 passengers?

Theory is one thing, and that is fine, but experience is an altogether different beast.

When many of us older guys came into the industry there were plenty of old sparks knocking about who had no formal qualifications as we know them, they had spent about 6 years learning the trade the hard way with sparks and were deemed to be competent to do the work. Paperwork is only a small part of the equation, practical experience and knowledge is the KING...
 
OK so 198 is below the allowed 200, but it will increase as the ground dry's up right?, so that 198 will almost certainly take the Ra/Ze to over 200. (whats the difference between Ra/Ze btw, are these terms interchangable?) Could you provide a 2nd parallel path for the rod maybe? I'm not sure.
nice recovery
 
OK so 198 is below the allowed 200, but it will increase as the ground dry's up right?, so that 198 will almost certainly take the Ra/Ze to over 200. (whats the difference between ra/ze btw, are these terms interchangable?) Could you provide a 2nd parallel path for the rod maybe? I'm not sure.
Which proves my point. Once again I'm not raining on your parade mate, just trying to give a reality check.
Let me put it another way, you're looking to change accountants. You speak to one who has years of experience and all the relevant memberships of the right associations and who assures you he has all the necessary skills to make sure you pay the right amount of tax and keep your accounts in proper order. The other says "I've done a six week course and that qualifies me to do personal tax but nothing else. Personal tax is pretty easy"
Which one gets to do your end of year return?
Do a search on here on TT systems and you'll get your answer.
 
have to say you are obviously no fool and have taken everything on board (unlike most we have on here from thee courses) stay on the forum and any question you have if I can help I will good luck.
 
OK so 198 is below the allowed 200, but it will increase as the ground dry's up right?, so that 198 will almost certainly take the Ra/Ze to over 200. (whats the difference between Ra/Ze btw, are these terms interchangable?) Could you provide a 2nd parallel path for the rod maybe? I'm not sure.

I would direct your attention to;

Chapter 41 Reg 411.5 TT pp57
Chapter 54 Reg 542.1.2.3 pp158
Chapter 54 Reg 542.2 pp159

if your 6 week course was any good (hahahahaha) then you should be able to figure out the solution to your dilemma.
 
Nice one Stuart, no doubt i'll be bending your ear in future. :smilewinkgrin:

Ok, so i just searched TT systems and it seems that on wet ground an Ra over 100Ω is not good and below 100Ω should be expected. 1667Ω !! is the maximum for a 30mA RCD. In future then should I Ra/Ze test on a TT and get over 100Ω on damp/wet ground then i'll inspect further, maybe corroded or otherwise damaged cpc cabling or connections.
 
Nice one Stuart, no doubt i'll be bending your ear in future. :smilewinkgrin:

Ok, so i just searched TT systems and it seems that on wet ground an Ra over 100Ω is not good and below 100Ω should be expected. 1667Ω !! is the maximum for a 30mA RCD. In future then should I Ra/Ze test on a TT and get over 100Ω on damp/wet ground then i'll inspect further, maybe corroded or otherwise damaged cpc cabling or connections.

Make sure you read it all properly and fully understand it...

You should always endeavour to get the RA as low as practicable, even if this means using multiple rods screwed together and hammered multiple meters into the ground..
 
I've just about read all the way through this thread and others like it and IMO what seems to clearly be lacking from the 5wws who are let loose on the general public is confidence, knowledge, some times attitude perhaps other things as well, all of this comes with experience. To sum up it's like allowing an apprentice "out on his own" well before he's ready. These Electrical Trainee should not be allowed to be registered as sparks with any scam until they have gained enough confidence, knowledge and experience by working for "companies" for a minimum of 3 - 5 Years and then apply for scam registration (with other graded electricians giving them their recommendation) to be self employed. There has as long as I can remember been these sort of courses, many years ago we used to call them GTC's they had attended Government Training Courses for various reasons. However I cannot remember a large influx of them all going "self employed" one man bands and all that. The chaps I came across over many years, a few turned out to be very good sparks but that was the ones who learned from other time served men on the job. Some where absolute rubbish, no doubt they went on to other things like plumbers lol In short these scams for domestic installer or whatever they what to call themselves stinks.
 
Thanks for the info Outspoken. How I would approach Trevs initial problem of the 198Ω ra in the wet. With 542.2 in mind, consider possible alternative 'practicable' earthing arrangements, maybe an old (unused) water pipe is nearby or there is some kind of underground metalwork I can earth to. Most likely though, I'd check the cpc and rod for obvious signs of damage. If damaged, consider replacing like for like, new cpc and rod, might as well replace with longer rod if practicable. I mean i'm not 100% sure, but i'd cross ref against the regs to make sure my arranagement was legal (and permanent, so that should a further trade change things my earthing still remains) and not leave it until the Ra was below 100 wet.
 
Just get it sorted lol
Thanks for the info Outspoken. How I would approach Trevs initial problem of the 198Ω ra in the wet. With 542.2 in mind, consider possible alternative 'practicable' earthing arrangements, maybe an old (unused) water pipe is nearby or there is some kind of underground metalwork I can earth to. Most likely though, I'd check the cpc and rod for obvious signs of damage. If damaged, consider replacing like for like, new cpc and rod, might as well replace with longer rod if practicable. I mean i'm not 100% sure, but i'd cross ref against the regs to make sure my arranagement was legal (and permanent, so that should a further trade change things my earthing still remains) and not leave it until the Ra was below 100 wet.
 
I've just about read all the way through this thread and others like it and IMO what seems to clearly be lacking from the 5wws who are let loose on the general public is confidence, knowledge, some times attitude perhaps other things as well, all of this comes with experience. To sum up it's like allowing an apprentice "out on his own" well before he's ready. These Electrical Trainee should not be allowed to be registered as sparks with any scam until they have gained enough confidence, knowledge and experience by working for "companies" for a minimum of 3 - 5 Years and then apply for scam registration (with other graded electricians giving them their recommendation) to be self employed. There has as long as I can remember been these sort of courses, many years ago we used to call them GTC's they had attended Government Training Courses for various reasons. However I cannot remember a large influx of them all going "self employed" one man bands and all that. The chaps I came across over many years, a few turned out to be very good sparks but that was the ones who learned from other time served men on the job. Some where absolute rubbish, no doubt they went on to other things like plumbers lol In short these scams for domestic installer or whatever they what to call themselves stinks.

You know what KAS1, give me a trainee job at 32 and i'll go with it. The reality is that most sparks would prefer a much younger trainee/apprentice (i guess because they feel they learn quicker). I'm far brighter than most 18 years olds, I understand this stuff and WANT to have it. If I could get a job at £10ph as a mate, i'd do it all day long. I can't. So finding the business for myself is my other option. As I said to Trev earlier on the thread though, my plan is not to go into a job by myself but to approach local spark with the lead and go along, as a trainee i'd then split the invoice 70/30 in their favour.
 
You know what KAS1, give me a trainee job at 32 and i'll go with it. The reality is that most sparks would prefer a much younger trainee/apprentice (i guess because they feel they learn quicker). I'm far brighter than most 18 years olds, I understand this stuff and WANT to have it. If I could get a job at £10ph as a mate, i'd do it all day long. I can't. So finding the business for myself is my other option. As I said to Trev earlier on the thread though, my plan is not to go into a job by myself but to approach local spark with the lead and go along, as a trainee i'd then split the invoice 70/30 in their favour.

OK, as long as you provide the mats :smart:
 

OFFICIAL SPONSORS

Back
Top