dave19

Hi Guys,

Working on a commercial site. We have been installating ACM's (Active Control Modules) for normal and emergency lighting. Inside the boxes where all the connections are I see that there is a link between the two neutrals. Why is there a link ?

Ta.
 
Unless there are two supplies or two RCD’s neutrals should be continuous. What are the supply conditions?
A link is often fitted for thesting. Have a look in the commecial section for "Scrambled Brains". E54 has flagged up some of the problems.
 
Unless there are two supplies or two RCD’s neutrals should be continuous. What are the supply conditions?
A link is often fitted for thesting. Have a look in the commecial section for "Scrambled Brains". E54 has flagged up some of the problems.

Hi Tony,

Yeah, I think it's a neutral in and out to the next ACM come to think of it. I take it they should be continuous in this situation ?
 
You mean a link from the neutral in and out?...

A bolted copper link?...would be better with a picture but if it's what I think you mean it's to isolate the neutral (once the phases are isolated of course), for testing purposes etc...

Quite common in large isolators, panels etc...