What current does the neutral take on a 3 phase system? For example if each line conductor pulls 100A, what does the neutral pull? Obviously not 300A, Bit confused, don't really work on 3 phase much.
Thanks guys, often wondered, but never asked. Glad I did now. So if an installation was severely imbalanced I guess this could cause over heating in the neutral conductor?
In=√(Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic))
So say:
Ia=65A, Ib=80A, Ic=40A In=35A