I've just had a new garden room done with electrics supplied via armoured from main house supply. Due to lack of space in the CU the electrician has put a mini CU in beside it (we now have three CUs as there's also one previously added for an EV charger). Garden room has its own 4 way CU for lights, sockets (incl external sockets), external lights, and air con.

The electrician tells me all this work does not require certification; is this correct?

As a second, lesser question, there is one 3 way light switch for the internal and external lights, it's a metal faceplate, with a terminal for an earth on it, however there is no earth cable attached, or run to the backbox; should there be? All the sockets appear to be earthed, as is the mini CU in the house, just this one light switch is without earth.

Thanks
 
ALL electrical work requires certification... either a new circuit, or an alteration to an existing circuit.

Metal faceplates should indeed be earthed.
 
I would seriously question this "electricians" competence on both counts.
 
Yes, Part pee and an installation cert, as said every bit of electrical work needs certifiying, even if it doesn't need part P, we've been asked for certs in the past when we've just replaced light fittings.

This may cause probelms when/if you sell the house, solicitors love delaying sales by asking for every bit of obscure paperwork, I read a thread the other day when the conveyancer was asking for the original planning permission document for a house built in the 50's.

Also if he's not in a scheme then what else has he cut corners on? If it was a youngish bloke dressed head to toe in snickers gear with brown/blue/earth sleeving tied to his belt then get it checked, if it was an older duffer dressed in scruffy clothes then it will probably be fine.
 
I had another electrician who is part of a scheme who has done work for me before take a look and he said the overall quality of the work carried out is good and it is tidy, but:

  • metal faceplate light switch needs earth
  • needs a switched fuse on the new mini CU inside the house (only a switch right now)
  • the 4 way CU in the room itself only has fuses not RCDs/RCBOs
  • needs EIC and part p cert as has been said here
 
Point 3 there may not need rcd protection in the garden room if the circuit it’s coming off already has it.
 
See attached.
 

Attachments

  • pic1.jpg
    pic1.jpg
    427.2 KB · Views: 121
  • pic2.jpg
    pic2.jpg
    684.3 KB · Views: 110
There should be another circuit breaker next to the 100amp main switch,possibly 16-32amp? As it is,the only thing protecting the swa cable is the 100amp main fuse.
 
Terrible job that was not done by a competent person. They way the blue is connected at those service terminal blocks is awful the blue should not be showing and it looks like the copper is exposed.
 
There should be another circuit breaker next to the 100amp main switch,possibly 16-32amp? As it is,the only thing protecting the swa cable is the 100amp main fuse.
This is what the other electrician I had look at it told me; said it should be replaced with something like this and likely 63A max but maybe less than that even.
 

Attachments

  • switfuse.png
    switfuse.png
    288.2 KB · Views: 107
And what about the monkey that did it and the lack of certification.
 