Evening guys,
Query with discrimination. Main DB with 30m/A RCD feeding another sub board with 30m\A RCD. The RCD in the main DB is tripping out before the sub board RCD. Am I able to change the Main DB RCD to a type S? (All that Main RCD is feeding is two sub boards, twin and earth fed in an office. Thanks in advance..
 
Is the t&e surface clipped or buried?
 
Then unless the cable is in earthed metallic protection or more than 50mm from the surface if in a wooden stud or in a metal stud then it requires additional protection by a 30mA RCD. You can’t get a type S 30mA RCD.
 
#5 You wouldn’t need the main RCD or you wouldn’t need the sub RCD?
It’s a two year old installation by the way. Was thinking about changing the main 30m/A RCD to a 100m/A type S but obv can’t because it need additional protection. Hmmmmm
 
If it's only a couple of years old sounds like poor design for a submain to require additional rcd protection. If it had been pre additional protection for cables in walls you may have had an argument although tenuous for removing it but as it stands it would be a bad idea.
 
You need to know what is causing the tripping fault or combined excess natural leakage. Is it both supplies or just one. Do you have an earth leakage clamp meter.
 

Reply to No Discrimination in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
481
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
793
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
242

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock