Your down to less than an ohm on your bonded pipe work?? lol!! Sorry i find that extremely hard to believe, in fact i'll go as far as saying, i don't believe it!!!!!!! So why is your earth rod only giving you an Ra of 120 ohms??
Ok, just done another test, and here are my results. Please tell me if I am doing something wrong.
Measuring Loop impedence L->PE with my probes on the tails going into the RCD for L and N, and the PE croc clip on the rod's earth cable disconnected from the MET I get 134 ohms. I put this bad reading down to it being an ancient thin twig you I can easily pull in and out of the ground by hand, and what looks like a very old 4mm earth conductor.
Measuring as above with the PE croc clip on the bond cable (which remember also has the buried copper pipe on it), I get 0.35 ohms (PFC 574A). I put this down to the copper in the hard clay earth underneath the house, metal gas pipe buried in the earth, and the fact that I am about 200 metres from the transformer. (just walked to the transformer and it is 173 paces with my little dwarf-legs)
hmm...well lets face it des...he should know that relying on extranious to bring down external loop isn`t on is itIts a long thread to read the full story
You have a high reading on your rod and have metal service pipes which gives a low Zs when connected
I know you say the transformer is nearby,is next door Pme ?
stroppy...what is it exactly your trying to acheave here mate?My gas pipe is definitely straight in the ground, as I can see it - its an ancient iron/steel thing that disappears into the earth. Anyway, I disconnected the bond from the gas pipe and still got 0.46, but then it ocurred to me: as the pipe is connected to appliances which have their metalwork earthed, am I not getting a parallel path through their CPC's? I'm not going to the trouble of disconnecting those, or the bonds on the water pipe or central heating as they are under the floor and a pain in the arse to get to. I'm getting more confused about this by the minute!
The more I think about it I think it is the gas service, as (a) it is a metal pipe going straight into the ground, and (b) the gas-main in the road goes right past the transformer within about 2 metres of it.
Testing the MET without the twig got me 0.35.
I'm not relying on it, I and E54 are just curious as to how it manages to be so low, and yes I know about parallel paths and the purpose of Ze thank you.hmm...well lets face it des...he should know that relying on extranious to bring down external loop isn`t on is it
we know this happens due to parallell paths but he should know the whole idea of doing a Ze in the first place...
if he cant fathom that one...then he`s no business testing ...has he...
how did you guess?...the cable ends were a bit scratchy mind on the way out but...I'm not relying on it, I and E54 are just curious as to how it manages to be so low, and yes I know about parallel paths and the purpose of Ze thank you.
As for can't fathom and no business testing, I presume you knew all about Zs Ze Ra parallel paths and testing as soon as you popped out of the womb, did you? No, you learnt it, which is what I'm doing.
Stroppy, if you're that close to your local tranny, fit an MET in your house, then run a 16mm cable from it to said transformer and bolt your cable onto it. Cover it over with dead leaves and other general detritus.
Should give you the best Ze in the area.

or the nearest lamppost....just wrap it round...a bit of a twist to get it tight....Stroppy, if you're that close to your local tranny, fit an MET in your house, then run a 16mm cable from it to said transformer and bolt your cable onto it. Cover it over with dead leaves and other general detritus.
Should give you the best Ze in the area.
If you had done the job properly and crimped on some round lugs poor Mumsie wouldn't have got scratched!!how did you guess?...the cable ends were a bit scratchy mind on the way out but...
well, thats what i was told anyway....
i think you`v been watchin too many reruns of the cristal maze....If you had done the job properly and crimped on some round lugs poor Mumsie wouldn't have got scratched!!