Lol, I just looked up the H&S requirements for this stuff and as suspected nothing to report, just use a bucket load of swafega and hot water. However, it is suggested that if ingested you should seek medical advice ?!!!.

I never considered that there might be any nutritional value in the gunky cloth/tape !
 
nah, tony's star/delta with a squirrel cage.

TonyCage.jpg

........
 
dig the garden then

Its going to down about metre so unless you're putting in the foundations for an extension then its unlikely to be affected. A loop measurement or better still, run your test electrodes across the lawn and into the next doors garden to get a resistance would be sufficient.

Alternatively use the exploration hole to wack in a 'twigg' and back fill with bentonite - Job done - lol
 
I do realise that the services are not there to be used as an earth, and the difference between earthing and bonding, which is why I started all this: testing the effectiveness of my earth twig. I will see if I can get PME'd, which would be the better option, otherwise I'll get some chunky rods and start driving them into the mud-bath that is my garden.

One day I'll get under the floor and individually test all the pipework and find which one is the culprit, but for now I CBA!

Regular viewers may remember this discussion about my pitiful 125 ohm reading from my earth rod (and unbelievably low Ze through the bonding). I know it is nice to have follow-up on discussions, so let's put this one to bed:

This afternoon I finished work at lunchtime and as, for once, it is not raining I thought I would sort out my earthing before I got cleaned up for the weekend. I have now pulled out my old 'twig' and pounded in two of Sarnia Electrical's finest shiny 3/8" earth rods and connected up my earthing conductor. Now I have a much more reasonable Ze of 44 ohms and a fault current of a whopping 5 amps.

That will do! As my late wife said, deeper is definitely better. :)
 