Hello to all, I went round to look at a job today, I thought i would check the Ze while i was there ! So i disconnected the 16mm earth from the consumer unit and then performed the test to find that the earth connected to the cut out did nothing at all! I could only get a reading from the parallel paths back from the gas and water bonds, I then thought i would try i quick Zs at the nearest socket (.21) That was fine because of the parallel paths,Do you think i should advise for a Pme to be fitted,
It looks like a cut out for TNS but there is no connection to the shealth of the incoming supply cable!