Mcnabb5

Hello to all, I went round to look at a job today, I thought i would check the Ze while i was there ! So i disconnected the 16mm earth from the consumer unit and then performed the test to find that the earth connected to the cut out did nothing at all! I could only get a reading from the parallel paths back from the gas and water bonds, I then thought i would try i quick Zs at the nearest socket (.21) That was fine because of the parallel paths,Do you think i should advise for a Pme to be fitted,
It looks like a cut out for TNS but there is no connection to the shealth of the incoming supply cable!
Regards.
 
well you have a tt system .either get in touch with supply authority and get it changed to TN-C-S which they have presented the cable head as or get an earth rod in making sure the rods reading is well under 200ohms and pu t in rcds.
 
Thanks for your quick resonse! The con unit looks like it has been changed quite recently! why didnt the other sparky see that it had no incoming earth? if it is a TT system there are no sign of any rods or earth going to ground! If i did an earth rod it would mean i would have to change the incomer to rcd, I think i will get the owner to get a pme it will work out cheaper! What do you think, regards!!
 
probably i dont know if the local electrical services woud charge to change to tncs i dont think so but if they did it should be around £200.
is it cheaper for you to fit an earth rod and 100ma rcd?
 
I aso believe you should consider an earth rod. Arranging the authority to change from TNS to TNCS could take some time, and some money !!!!
 
It is highly unlikely that the DNO would change from a TNS to TNCS as the facility would more than likely not be available on the network, although some are now installing TNS as opposed to PME.

The most common Earth upgrade is from TT to TNCS.
 