Sparktim

Hi all this is my first post hope you don't mind helping me out.



On a job I am doing there is only 1 ring for all the sockets inc kitchen it is a 4 bed house! When the ring is joined as a figure of eight in the db I get 0.29ohms but as I go round the house I only get a similar reading to this at 4 sockets. There is a lot of spurs and it seems to be a bit of a mess what
would you all do? The rest of the test are all good. I had to re wire a leg of this ring as it was cut by the plumber.


Thanks in advance

Tim
 
Last edited by a moderator:
Cheers for the reply i know what you mean. I just had to repair the damaged leg after the plumber cut it. I was thinking of just putting it on a 20amp mcb as I don't really want to adapt it to 2 sort of radials. Just a shame the whole house is on it.
 
If you are repairing a damaged cable this would be classed as maintenance,but you can always highlight your concerns with the customer and see how they want to proceed,you dont want to work for free!
 
The customer does not want to do too much as always! So if I leave it as is and fill out a minor works with my concerns on it i am covered?
 