E
Edd
Neither do they need them fitted. So the fine only stands if they are fitted.
As I said way missed the point!

Neither do they need them fitted. So the fine only stands if they are fitted.

When i do them if its rewirable and the bonding and the disconnection times are fine its a c3 with a recommend to change board.
As I said way missed the point!![]()
As I said way missed the point!![]()
thats wasted on some in here....did one today. had a look at selects guidance notes on inspections.
C3 for non rcd protected sockets.
thats their take on it anyway.
the problem with inspections is that the unexperienced are going in to do these jobs with no clue what is dangerous and what is not.
we did have electricity before the 17th you know.
When i do them if its rewirable and the bonding and the disconnection times are fine its a c3 with a recommend to change board.
if the disconnection times are pants c2 but usually that means there is other stuff going on and its unsatisfactory anyway.