UK Outdoor security light wiring

I am a trainee electrician and have nearly completed my level 2. Just curious as never come across it before but can I run a single length of 1mm T+E from my ceiling rose loop terminal to an outdoor security light and then rely on the pir to go on and off? I Don't want a switch.
 
Thanks westward, it's reassuring that my thoughts and plans are actually genuine and right. Obviously a lot to learn still but every day is a school day and I try and brush up the weak areas of my knowledge as much as I can! I've already realised there's a lot of crossover areas or grey areas where there is a lot of different opinions and ideas on certain things which obviously does confuse me but as long as what I do is safe and obviously within the regs I'm happy 👍
Exactly why I like this forum (and should use it more often). Even something as simple as supply to an outside light can require a lot of thought and consideration, and have more than one solution.
I've been in the trade 10 years now but always tend to learn things, big and small, whenever I log on.
 
I am a trainee electrician and have nearly completed my level 2. Just curious as never come across it before but can I run a single length of 1mm T+E from my ceiling rose loop terminal to an outdoor security light and then rely on the pir to go on and off? I Don't want a switch.
T&E cable isn't suitable for exposure to UV and therefore should not be used outside. You could run T&E to an external junction box and use a suitable cable from that point onwards.
Obviously, you'll need to test the circuit beforehand and ensure that the circuit including any addition is fully compliant with current regulations.
 
T&E cable isn't suitable for exposure to UV and therefore should not be used outside. You could run T&E to an external junction box and use a suitable cable from that point onwards.
Obviously, you'll need to test the circuit beforehand and ensure that the circuit including any addition is fully compliant with current regulations.
With all due respect you haven't read the full thread as I said it would join into a wiska box but yes the testing before is a good point 👍
 
UPDATE: after checking, there is no permanent supply into the ceiling rose so I'm now a bit stuck, it seems to be bridged at the switch for a mixture of 2 plate and 3 plate ? 🤔 Very old wiring within as well
 

Attachments

  • PXL_20250920_080336647.jpg
    PXL_20250920_080336647.jpg
    487.5 KB · Views: 13
  • PXL_20250920_080702423.jpg
    PXL_20250920_080702423.jpg
    765.1 KB · Views: 13
I wouldn't be touching that the circuit does not appear to incorporate cpcs. This is why to test first and not repent later.
 
I think I can see cpcs…. Plain green sleeving rather than green/yellow.

It’s possibly a central joint box system… so you’ll get a feed there.
Attic, or under the floor upstairs
 
I think I can see cpcs…. Plain green sleeving rather than green/yellow.

It’s possibly a central joint box system… so you’ll get a feed there.
Attic, or under the floor upstairs
Cps on the fitting but not at all switches, the switch in the picture switches the fitting in the picture so I'm sure it's fed from that switch due to the strapper if not why would there be 3 cables in the back of said switch 🤔 it's a 2 Way switch as well so 🤷‍♂️
 
I am a trainee electrician and have nearly completed my level 2. Just curious as never come across it before but can I run a single length of 1mm T+E from my ceiling rose loop terminal to an outdoor security light and then rely on the pir to go on and off? I Don't want a switch.
Yeah, that should be fine as long as the PIR’s wired for a permanent live and switched output. We usually run the feed through the PIR to make things easier later on.
 
Last edited by a moderator: