Can anyone help since the summer is coming when my solar started to rise is seems that I am using more eletric , I.e solar at 3.70 kW and my energy used is around the same can anyone help
 
Yes I have done that , I have taken the clip off the eletric box and I am still getting a reading

Hi Twindecks. The most likely issue is that the CT clamp on the supply live tail needs to be flipped over so that it faces the other way around.

One of the two clamps measuring solar generation should be linked to the CT clamp on your supply live using a "Y" cable.

The CT clamp that is on the supply live must face in the opposite direction to the CT clamp on the the PV live otherwise the device adds the generation to the amount used from the grid rather than taking it away.

It is generally easier to access the CT clip on the supply live rather than on the PV live hence my suggestion.

All you need to do unclip the CT clamp, turn it 180 degrees and then clip it back on.

I hope this helps.

Andrew
 

Reply to owl Pv intuition in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
923
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
779
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi, I have a 6kw PV with a 6kw Growatt battery and invertor. I have a solar iboost going to the hotwater tank. Recently I had a Ohme Home Pro...
Replies
2
Views
2K
Hi, We're looking at installing solar at a remote property which is on a TT system with out buildings supplied with underground cables (Stables...
Replies
1
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock