Hi,

My lighting circuits are on 6A breaker, and my existing DETA pendant fixings with flex are rated by the manufacturer at 6A, I use 13W LED bulbs.

I have found a good quality alternative from Scolmore Click Polar and they are only rated at 2A by the manuafcturer, would it be OK to fit the Scolmore ones, the cabling is actually thicker and better quality and the ends of the stranded ferulled?

Thanks,
James.
 
The 6A covers the entire circuit. The pendant is rated for only what is plugged into its lampholder.

Even an old 100W at 230V is less than half an amp load.
 