Discuss Pig tails EMC in the UK Electrical Forum area at ElectriciansForums.net

Agreed, coiling the CPC adds inductance and reduces the effectiveness of the CPC as a sink for RF interference. The text appears to have been translated, not very well, from another language. I wonder what the name for a pigtail is in the source language.
 
Agreed, coiling the CPC adds inductance and reduces the effectiveness of the CPC as a sink for RF interference. The text appears to have been translated, not very well, from another language. I wonder what the name for a pigtail is in the source language.

Yes, those instructions don't inspire much confidence in the product!
 
Oh okay another question while I’m on this topic is the manufacturer states to (ground the screening of the motor cable both ends motor > drive ) however they supply the cable with an exposed screen one end and the other end which they have heat shrunk. What is the benifit/disadvantage of earthing just one end or earthing both ends of the screen?
 
If you want a cable's braid screen to be effective then you need a low inductance connection (as other have said). The ideal is to use the equivalent of a SWA gland that provides a 360-degree connection from the shield to the (assumed!) metal box so you have the least possible inductance.

The "pig tail" is any sort of wire used to connect the braiding to earth. Obviously worse if coiled, but even a straight 5-10cm length has a massive effect at HF/VHF frequencies!

If you are using SY or CY cable for the motor connections then you can get glands for that sort of cable to both restrain and ground the shield, for example:

Sometimes SWA glands will do, but they don't always allow clamping of the much thinner braid on the SY/CY style of cables.

(Yes, it is often discussed how SY, etc, are not BS standard and generally not UV resistant so should not be used for fixed power, etc, but for the output of VFD they are often a very good choice due to the braid screening and relative flexibility).
 
We don't use them but I've seen them on some booster pumps and was curious as to how you got on with them ? We use ABB normally which are pretty easy to set up.
If you want a cable's braid screen to be effective then you need a low inductance connection (as other have said). The ideal is to use the equivalent of a SWA gland that provides a 360-degree connection from the shield to the (assumed!) metal box so you have the least possible inductance.

The "pig tail" is any sort of wire used to connect the braiding to earth. Obviously worse if coiled, but even a straight 5-10cm length has a massive effect at HF/VHF frequencies!

If you are using SY or CY cable for the motor connections then you can get glands for that sort of cable to both restrain and ground the shield, for example:

Sometimes SWA glands will do, but they don't always allow clamping of the much thinner braid on the SY/CY style of cables.

(Yes, it is often discussed how SY, etc, are not BS standard and generally not UV resistant so should not be used for fixed power, etc, but for the output of VFD they are often a very good choice due to the braid screening and relative flexibility).
So best practice is 360degree at both ends of the motor cable?
 
So best practice is 360degree at both ends of the motor cable?
Yes, if you can use glands that clamp the braid and they are on metal boxes (ideally using Earthing / Piranha nuts for good connetion to box, not relying on a cm or so of banjo) then you get the best EMC protection.

If the box is plastic (or otherwise non-conductive / not-connected) then you have your earth flying lead anyway so the majority of EMC benefits are lost. But the braid (or armour) obviously has to be earthed/chassis connected for safety by some means.
 

Reply to Pig tails EMC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Had a call out to a tripping issue yesterday. I found that the very old RCD was faulty, but upon inspection something didn't look right regarding...
Replies
17
Views
738
Hi all. I am installing some metal trunking vertically in a meter cupboard to contain all the meter tails for an apartment block. I have 5 sets...
Replies
1
Views
595
Can I install an RFI / EMI filter (designed to increase efficiency with a photvoltaic (PV) solar energy inverter) to an existing solar system...
Replies
1
Views
940
On a domestic Cu 60 amp would live and nuetral tails cause eddi currents of any significants if the tails were run in sperate metal conduit but...
Replies
4
Views
675
See attached photo of my new 3 phase supply at my house. Tails supply a Schneider 3ph board. Sparky is in two minds about the correct earthing...
Replies
11
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock