Plug in solar with a ring final?

E

EricMark

1774524252807.png
I know this is unlikely, but it shows how we could have 35 amp on a cable designed for 20 amps, why has plug in solar been allowed? I can see with a radial system as used in the rest of Europe that a 20 amp cable with a 16 amp overload that cable is unlikely to be overloaded, but with the British ring final, it can cover a far bigger area, so more likely to have multi plug in solar devices. Having a plug on the supply was always called the widow maker, with say 4 plug in solar arrays into one extension lead, are we sure there will be no islanding?
 
View attachment 124539I know this is unlikely, but it shows how we could have 35 amp on a cable designed for 20 amps, why has plug in solar been allowed? I can see with a radial system as used in the rest of Europe that a 20 amp cable with a 16 amp overload that cable is unlikely to be overloaded, but with the British ring final, it can cover a far bigger area, so more likely to have multi plug in solar devices. Having a plug on the supply was always called the widow maker, with say 4 plug in solar arrays into one extension lead, are we sure there will be no islanding?
AI tells me: "The legal change is expected to permit plug-in systems with a maximum capacity of 800W" which is presumably where the 3.5A comes from? Will more than one be permitted (though how would you ensure that - perhaps through inverter design?)
I wonder how safety (eg the widow maker) will be ensured!
 
Last edited:
View attachment 124539I know this is unlikely, but it shows how we could have 35 amp on a cable designed for 20 amps, why has plug in solar been allowed? I can see with a radial system as used in the rest of Europe that a 20 amp cable with a 16 amp overload that cable is unlikely to be overloaded, but with the British ring final, it can cover a far bigger area, so more likely to have multi plug in solar devices. Having a plug on the supply was always called the widow maker, with say 4 plug in solar arrays into one extension lead, are we sure there will be no islanding?
Some sort of overload protection may help with that sort of scenario.
 
the "widow maker" scenario will be like any invertor... it wont feed back unless it senses a live feed....

Although.... with more than one plug in.... would each unit just sense the other and continue to feed in.... even with the grid disconnected?


This is going to make safe isolation a nightmare.... half the customers don't know what they've got plugged in most of the time anyway...

"have you unplugged everything like i asked? my tester is still reading a short....."

"yes..... everything except the fridge freezer... the kettle, the tv... "
 
the "widow maker" scenario will be like any invertor... it wont feed back unless it senses a live feed....

Although.... with more than one plug in.... would each unit just sense the other and continue to feed in.... even with the grid disconnected?


This is going to make safe isolation a nightmare.... half the customers don't know what they've got plugged in most of the time anyway...

"have you unplugged everything like i asked? my tester is still reading a short....."

"yes..... everything except the fridge freezer... the kettle, the tv... "

I spoke with the IET and the niceic at the elex show today at ally pally.

They both said Ed Milliband has no idea what he's talking about and they are waiting and seeing what the review says
 
I spoke with the IET and the niceic at the elex show today at ally pally.

They both said Ed Milliband has no idea what he's talking about and they are waiting and seeing what the review says
Thank you, it would seem it is all aimed at rental property, so one can move and take it with you. With owner occupied, there is simply no need for plug and play, one has always been able to fit solar with the G98 or G99 route.

What I have been unable to work out, is how the CT coil is housed? The adverts show a Shelly unit which is din rail mounted and mains powered so not really plug and play, I would have expected something like the unit used with the iboost+ that simply clips over the supply tail, and is battery powered.

I know with my own solar panels, it is not just the panels, but a complete package which makes it work, so overnight the battery is charged, then as off-peak ends I start using the battery, until the sun comes out, and solar takes over and recharges the battery, and then once battery is fully charged it starts to export, and as the sun shine debates we start using the battery again until off-peak returns.

There is no limit even with plug in solar on the battery size, or solar panel size, the limit is on how much can be fed into a 13 amp outlet.
 
the "widow maker" scenario will be like any invertor... it wont feed back unless it senses a live feed....

Although.... with more than one plug in.... would each unit just sense the other and continue to feed in.... even with the grid disconnected?
Unlikely to happen, They monitor the grid for abnormal conditions, If the grid goes down they all go down.
 
Unlikely to happen, They monitor the grid for abnormal conditions, If the grid goes down they all go down.
Thank you, it would seem it is all aimed at rental property, so one can move and take it with you. With owner occupied, there is simply no need for plug and play, one has always been able to fit solar with the G98 or G99 route.

What I have been unable to work out, is how the CT coil is housed? The adverts show a Shelly unit which is din rail mounted and mains powered so not really plug and play, I would have expected something like the unit used with the iboost+ that simply clips over the supply tail, and is battery powered.

I know with my own solar panels, it is not just the panels, but a complete package which makes it work, so overnight the battery is charged, then as off-peak ends I start using the battery, until the sun comes out, and solar takes over and recharges the battery, and then once battery is fully charged it starts to export, and as the sun shine debates we start using the battery again until off-peak returns.

There is no limit even with plug in solar on the battery size, or solar panel size, the limit is on how much can be fed into a 13 amp outlet.
I wonder how many cable ties you get in the kit to enable you to latch on to the balcony and are the cable ties MCS approved. It makes a mockery out of the whole Solar Industry.
 
I wonder how many cable ties you get in the kit to enable you to latch on to the balcony and are the cable ties MCS approved. It makes a mockery out of the whole Solar Industry.
The plugs are monitored, the inverter shuts off as soon as it looses connection , so before the pins clear the socket. Efixx did some videos of it. The panels I have seen featured have integrated clamps which fix to railings or angled frames, not tyewraps. The solar industry has been taking the ---- with their prices and practices. The IET and niceic are just making things up as they go along, tbey didn't even realise that most of the homes on the Eco3-4 scams are covered in foam until I told them at a Elex Q&A last year when they were pushing solar and battery storageThese are the people who thought it was ok to put inverters and batteries in the loft originally.
 
I can go to a UK shop and buy a transceiver using 144 MHz without showing a licence, but if I want to buy a gun, I need a licence, even when both need a licence to use them.

So being able to buy a kit in a UK shop, does not mean you can use it. I have bought a gas boiler before now, OK I was not fitting it, but there was no check as to if I was licensed to fit it.

And this I see as the problem with plug in solar, we have had media coverage about how it is going to be allowed, and there has been a flood of internet adverts for plug in solar,
1775996704110.png
and some is legal and some is not. There is nothing to stop one having a battery pack and solar and powering devices directly from the battery pack, but the advert shown, seems to have no battery pack, and the data sheet says Schuko plug fitted, and address given for the company is Northampton, in other words it is British.

How can it comply with British regulations when as yet not published? Any home user could simply assume it has now all been passed, and there is nothing wrong with using it on their rented accommodation, at £158.76 I will admit I am tempered, maybe fit a couple, OK I can do the maths, 800 watt will likely give 800 kWh per year, at £0.12 per kWh so £96 per year, so should pay for its self in 2 years.

I already have solar, so I know 6 kW of panels has given me 5 MWh first full year, and 6 MWh last year, and since I already have the second MPAN number, I will get paid for export, as no one will know I have them, so nothing forcing me to complete another G98.

Only reason not to get them, is I am not sure my handrails on my balcony will take the weight.
 
1776158918700.png

I think its make your mind uptime, one minute they want more solar, the next they want less.
 
Plug and play is not installed, so not covered by BS 7671, "The Electrical Equipment (Safety) Regulations 2016" say "(2) These Regulations do not apply to— (e)plugs and socket outlets for domestic use; " and I am left wondering it they are illegal?
 
Plug and play is not installed, so not covered by BS 7671, "The Electrical Equipment (Safety) Regulations 2016" say "(2) These Regulations do not apply to— (e)plugs and socket outlets for domestic use; " and I am left wondering it they are illegal?
Try sticking a PAT tester on it.....


I suppose these things could be a good idea for camping, caravans etc, but they should be hard wired... no plug... and the same regulations that cover roof mounted PV.... dedicated RCD, isolators etc...
 
I agree, solar panels need to be regulated, but it was not myself who said they will be allowed, it was Edward Miliband who has decreed they will be permitted this summer.

There is a whole list of objections, but the major one is the supply meter must be able to work with them. As it stands we have a load of old meters, some register electric passing through them, it does not matter which direction, so plug and play solar could increase the bill, so will actually go backwards, so the user is paid same for import and export, some just show an error light for export, and some have two registers one for import and one for export.

I think his only option would be to say can only be used when a smart meter is installed. Also needs permission from landlord and insurance, and would need to comply with some British standard.

G98 will not work, as it is non-transferable, the whole idea of plug and play is it can be taken home to home, and is not installed.

Meteorological summer runs from 1 June so we only have 4 weeks before it is to be released, and we are already seeing people jump the gun, how those people will get retrospective approval I don't know, and if someone is injured after 1 June who will go to court, Edward Miliband?
 
I note:- "BS1363-1
4 General
Plugs shall be so designed and constructed that in normal use their performance is reliable and minimises the risk of danger to the user or to the surroundings. Such plugs shall be capable of meeting all the relevant requirements and tests specified in this part of BS 1363. Plugs shall not be used for the connection of electrical power generators to socket-outlets."

So not with 13 amp socket, but could use the socket for EV charging.

What for me would cause a problem is so much solar that it is actively discouraged by reducing the export tariff. Or causes black-outs due to lack of rotating mass.

The problem is no one knows how much solar is being produced, it is simply seen as a load reduction, OK, the smart meter may register what I export, but not what I store and use within the home and any solar not registered will make that worse.
 