I am about to install 4 sockets in 4 separate stone enclosures, housed within a large stone outbuilding. They have stone floors and are completely weatherproofed. They may be having small animals in them, goats, sheep etc.

The existing set up is TN-C-S.

BS7671 doesn't go into much depth with regards earthing. 705.411.4 just says a TN-C system shall not be used. Does this mean just TN-C, or does it also mean TN-C-S? It's a little confusing as the title to this regulation is TN system.

Is the thinking that there may be some potential between the PME earth and actual earth and that this potential could become lethal to livestock? Is this more likely in muddy, wet, earth floored barns or is it just as relevant in my situation above (all stone).

The existing electrical system has been very well installed, which leads me to think this has been thought out, as it must have been installed whilst this regulation was in practise...... making me think perhaps it doesn't need a TT for some reason. Here is a picture of the supply...

PME on a farm?........... 3 phase supply - EletriciansForums.net
 

loz2754

-
Esteemed
Arms
Reaction score
3,938
Thought that picture was familiar:

 
OP
HappyHippyDad

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,290
The note, just below this reg, says "This does not preclude the use of TN-C-S."
Just realised I was looking in the Big blue, not the Big brown.
So this suggests it may be ok to use PME.
However, they recommend at earth grid is laid.
So really, TN-C-S is not going to be used if all the ground work is already laid?
 
OP
HappyHippyDad

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,290
Thought that picture was familiar:

It is rather nice to look at though 😀

I don't know what it is about it, but it makes me feel calm.
 

Reply to PME on a farm?........... in the Electrical Forum area at ElectriciansForums.net

Similar Threads

This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
1K
After conducting a recent EICR I found among other things that the Galvanised columns in the carpark area of this premises seem to be connected...
Replies
10
Views
989
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
764
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
1K

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top