If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
I am about to install 4 sockets in 4 separate stone enclosures, housed within a large stone outbuilding. They have stone floors and are completely weatherproofed. They may be having small animals in them, goats, sheep etc.

The existing set up is TN-C-S.

BS7671 doesn't go into much depth with regards earthing. 705.411.4 just says a TN-C system shall not be used. Does this mean just TN-C, or does it also mean TN-C-S? It's a little confusing as the title to this regulation is TN system.

Is the thinking that there may be some potential between the PME earth and actual earth and that this potential could become lethal to livestock? Is this more likely in muddy, wet, earth floored barns or is it just as relevant in my situation above (all stone).

The existing electrical system has been very well installed, which leads me to think this has been thought out, as it must have been installed whilst this regulation was in practise...... making me think perhaps it doesn't need a TT for some reason. Here is a picture of the supply...

3 phase supply.jpg
 
Just to add that TN-C is exceedingly rare, as the protective earth and the neutral are connected together throughout the system.
 
  • Like
Reactions: Baddegg
There is note 2 to 705.415.2.1 to consider:

Unless a metal grid is laid in the floor, the use of a PME earthing facility as the means of earthing for the electrical installation is not recommended
 
The note, just below this reg, says "This does not preclude the use of TN-C-S."
Just realised I was looking in the Big blue, not the Big brown.
So this suggests it may be ok to use PME.
However, they recommend at earth grid is laid.
So really, TN-C-S is not going to be used if all the ground work is already laid?
 
It is rather nice to look at though 😀

I don't know what it is about it, but it makes me feel calm.

It's a bit of a poor job, there's a lot of unsupported cables for starters.

With a bit of thought, and some containment it could have been a lot better.
 
  • Agree
Reactions: UNG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
PME on a farm?...........
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
davesparks,
Replies
7
Views
3,544

Advert