You will find that you have to be quite careful of the wording on this forum otherwise you get pounced on by the bully boys
More like Collins dictionary boys, that word does not exist, it does now.
 
The original post said nothing about specific factors. So unless it's a metal container, swimming pool, caravan or some other type of special location there are no regs saying it can not be exported.
Nobody said any different.
 
It has already been mentioned on here that you are not 'EXPORTING' TN-C-S you are utilising a cpc derived from a TN-C-S earthing system.
 
It has already been mentioned on here that you are not 'EXPORTING' TN-C-S you are utilising a cpc derived from a TN-C-S earthing system.
 
Another misworded publication. The schemes actively promote the term 'exporting'.
 
  • Like
Reactions: loz2754 and DPG
Tim at post #33

Exporting a PME earth isn't as simple as you suggest, as there will be a number of factors that have to be taken into account, depending on its use.
You wouldn't want to be running a 16mm 3 core swa to a customers wooden potting shed that is 2mtrs away, has no extraneous earths and has just one lighting point.

On the other hand, you wouldn't want to export to a cattle shed.




Not saying you would, but you could.
 
It has already been mentioned on here that you are not 'EXPORTING' TN-C-S you are utilising a cpc derived from a TN-C-S earthing system.
Semantics.
 
  • Agree
Reactions: mainline
Maybe but to export it you would have to do exactly that. The fact that you could have a 'special location' downstream in some cases may not be relevant. I could have a bathroom in this downstream location but could still employ the TN-C-S derived earth.
 
Maybe but to export it you would have to do exactly that. The fact that you could have a 'special location' downstream in some cases may not be relevant. I could have a bathroom in this downstream location but could still employ the TN-C-S derived earth.
Having a bathroom on a TNCS is fine as long as you keep to the regs but there are some special locations where a TNCS can not be used.
 
Yes I realise this hence why I said in some cases.
 
Having a bathroom on a TNCS is fine as long as you keep to the regs but there are some special locations where a TNCS can not be used.
Are we going from Exporting to sheds or out buildings or bathrooms.lm getting confused!!.
 
@default I was referring to your #35.
 
But in post #47
You said you could ?

Are you not reading all of the posts ?
I was referring to the main point of the post which was about the potting shed.
 
You will find that you have to be quite careful of the wording on this forum otherwise you get pounced on by the bully boys 🤣
@default my apologies if it came across as bullying. I'm always conscious people search this forum for advice and thought it a little dangerous to leave the word "isolator" in there. And it could have been construed to mean a "sub-main" never needs an RCD.
Anyway, nothing personal! I'm sure most of us knew what you meant, the concern was a DIY hero reading it.
 
@default my apologies if it came across as bullying. I'm always conscious people search this forum for advice and thought it a little dangerous to leave the word "isolator" in there. And it could have been construed to mean a "sub-main" never needs an RCD.
Anyway, nothing personal! I'm sure most of us knew what you meant, the concern was a DIY hero reading it.
I wasn't referring to you Tim 🤣
 
  • Thanks
Reactions: timhoward
Maybe but to export it you would have to do exactly that. The fact that you could have a 'special location' downstream in some cases may not be relevant. I could have a bathroom in this downstream location but could still employ the TN-C-S derived earth.
The way I see it is this :
if you have a tnc-s /pme earthing system, and it is taken to an outbuilding that is out of the equipotential zone of the property then you would be exporting it.

If the building is within that zone and no extraneous, then you would be utilising the cpc.
 
Last edited:
I think a lot of the confusion surrounding this comes from the word 'export'.
Thank you. The word "export" makes me cringe every time!

The way I see it is this :
if you have a tnc-s /pme earthing system, and it is taken to an outbuilding that is out of the equipotential zone of the property then you would be exporting it.
The way I see it is that we are excellent at over-thinking this topic.

-We are creating a distribution circuit.
-Normal fault protection rules apply
-Normal RCD selectivity rules apply
-Whatever the earthing is at the origin will be the earthing for the distribution circuit unless we deliberately change it.
-There might be stuff to bond the other end, in which case normal bonding rules apply including the size of the CPC that supports it (noting new AM2 reg about bonding conductor sizes in a separate building)
-As with all installation work, special location rules can apply

In my experience most of the time this all amounts to "carry on".
And don't let the OpenPen doom angels deter you! I'd bet it's more likely the never-tested RCD will fail on a TT setup than an OpenPEN fault happening to that very house.
 
@mainline can you say where in BS7671 they reference equipotential zone and then further support your statement.
 
  • Like
Reactions: loz2754
@mainline can you say where in BS7671 they reference equipotential zone and then further support your statement.


As said, it's how I differentiate between the word "utilise" and “export”.

The word "export " is recognised and used by all the schemes, and everyone understands the meaning.
 
Equipotential zone is what you need to clarify.
 
Equipotential zone is what you need to clarify.
You want me to give explain what equipotential zones are ? And the risk of step potential ?

Just because its the way i differentiate between extending, utilising and exporting is not to your liking, then maybe you can explain it.
 
Last edited:
Just wondered as that term hasn't been used in BS7671 for many a year.
 
Just wondered as that term hasn't been used in BS7671 for many a year.
Do you mean The term “equipotential zone” hasn't been used ? Does that mean Equipotential zones no longer exist, I thought you create an equipotential zone when you equipotential bond which I think there maybe a mention of in bs7671. 😯
 
Last edited:
Do you mean The term “equipotential zone” hasn't been used ? Does that mean Equipotential zones no longer exist 😯
Do you mean The term “equipotential zone” hasn't been used ? Does that mean Equipotential zones no longer exist 😯
Wow an argument about wording on this forum. Will wonders never cease. 😄
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Assistance with my installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
70

Advert

Thread statistics

Created
Poacher3536,
Last reply from
default,
Replies
70
Views
7,619

Advert