Maybe but to export it you would have to do exactly that. The fact that you could have a 'special location' downstream in some cases may not be relevant. I could have a bathroom in this downstream location but could still employ the TN-C-S derived earth.
The way I see it is this :
if you have a tnc-s /pme earthing system, and it is taken to an outbuilding that is out of the equipotential zone of the property then you would be exporting it.

If the building is within that zone and no extraneous, then you would be utilising the cpc.
 
Last edited:
I think a lot of the confusion surrounding this comes from the word 'export'.
Thank you. The word "export" makes me cringe every time!

The way I see it is this :
if you have a tnc-s /pme earthing system, and it is taken to an outbuilding that is out of the equipotential zone of the property then you would be exporting it.
The way I see it is that we are excellent at over-thinking this topic.

-We are creating a distribution circuit.
-Normal fault protection rules apply
-Normal RCD selectivity rules apply
-Whatever the earthing is at the origin will be the earthing for the distribution circuit unless we deliberately change it.
-There might be stuff to bond the other end, in which case normal bonding rules apply including the size of the CPC that supports it (noting new AM2 reg about bonding conductor sizes in a separate building)
-As with all installation work, special location rules can apply

In my experience most of the time this all amounts to "carry on".
And don't let the OpenPen doom angels deter you! I'd bet it's more likely the never-tested RCD will fail on a TT setup than an OpenPEN fault happening to that very house.
 
@mainline can you say where in BS7671 they reference equipotential zone and then further support your statement.
 
  • Like
Reactions: loz2754
@mainline can you say where in BS7671 they reference equipotential zone and then further support your statement.


As said, it's how I differentiate between the word "utilise" and “export”.

The word "export " is recognised and used by all the schemes, and everyone understands the meaning.
 
Equipotential zone is what you need to clarify.
 
Equipotential zone is what you need to clarify.
You want me to give explain what equipotential zones are ? And the risk of step potential ?

Just because its the way i differentiate between extending, utilising and exporting is not to your liking, then maybe you can explain it.
 
Last edited:
Just wondered as that term hasn't been used in BS7671 for many a year.
 
Just wondered as that term hasn't been used in BS7671 for many a year.
Do you mean The term “equipotential zone” hasn't been used ? Does that mean Equipotential zones no longer exist, I thought you create an equipotential zone when you equipotential bond which I think there maybe a mention of in bs7671. 😯
 
Last edited:
Do you mean The term “equipotential zone” hasn't been used ? Does that mean Equipotential zones no longer exist 😯
Do you mean The term “equipotential zone” hasn't been used ? Does that mean Equipotential zones no longer exist 😯
Wow an argument about wording on this forum. Will wonders never cease. 😄
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Assistance with my installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
70

Advert

Thread statistics

Created
Poacher3536,
Last reply from
default,
Replies
70
Views
7,695

Advert