Maybe but to export it you would have to do exactly that. The fact that you could have a 'special location' downstream in some cases may not be relevant. I could have a bathroom in this downstream location but could still employ the TN-C-S derived earth.
The way I see it is this :
if you have a tnc-s /pme earthing system, and it is taken to an outbuilding that is out of the equipotential zone of the property then you would be exporting it.
If the building is within that zone and no extraneous, then you would be utilising the cpc.
I think a lot of the confusion surrounding this comes from the word 'export'.
Thank you. The word "export" makes me cringe every time!
The way I see it is that we are excellent at over-thinking this topic.
-We are creating a distribution circuit.
-Normal fault protection rules apply
-Normal RCD selectivity rules apply
-Whatever the earthing is at the origin will be the earthing for the distribution circuit unless we deliberately change it.
-There might be stuff to bond the other end, in which case normal bonding rules apply including the size of the CPC that supports it (noting new AM2 reg about bonding conductor sizes in a separate building)
-As with all installation work, special location rules can apply
In my experience most of the time this all amounts to "carry on".
And don't let the OpenPen doom angels deter you! I'd bet it's more likely the never-tested RCD will fail on a TT setup than an OpenPEN fault happening to that very house.
@mainline can you say where in BS7671 they reference equipotential zone and then further support your statement.
As said, it's how I differentiate between the word "utilise" and “export”.
The word "export " is recognised and used by all the schemes, and everyone understands the meaning.
Equipotential zone is what you need to clarify.
You want me to give explain what equipotential zones are ? And the risk of step potential ?
Just because its the way i differentiate between extending, utilising and exporting is not to your liking, then maybe you can explain it.
Just wondered as that term hasn't been used in BS7671 for many a year.
Do you mean The term “equipotential zone” hasn't been used ? Does that mean Equipotential zones no longer exist, I thought you create an equipotential zone when you equipotential bond which I think there maybe a mention of in bs7671. 😯
Poacher3536,
default,