Hi guys, I've been asked to put power in a garden shed (5m x 3m) Next to the CU (6 way) is a small 2 way box wired via Henley block to meter (this was used for an old oven but is not used any more). I was thinking of putting a 40amp MCB in this board and running armoured (4mm) cable through wall and down side of house, then through hedge (at ground level) to shed ( a distance of 50m) pop a board in shed with RCD, a 6amp for lights and a 32amp for a small ring (3 double sockets). Does this sound OK. anything I need to change or look out for. Many thanks guys.
 
'Through the hedge' doesnt sound ok.....ideally bury it. What is your expected demand?....50m with a 4mm might leave you with volt drop issues if you are thinking a 40a supply is necessary.
 
Design current of 38A, a run of 50m?, you're probably looking at 16mm SWA and a restriction on the lighting load.
 
Hi checked volt drop on TLC web site. Shed is going to be a gym ( so probably never used) with a tread mill which uses 700 watts a small TV and radio plugged in plus a couple of strip lights, so not a lot.
 
If trying to reduce csa of SWA, reduce the design current. 3A breaker for your light, 10A breaker for your socket, you should be able to use 6mm, though you need to verify these calcs yourself.
 
OK need to have a rethink. Anything else guys. All Ok to use second board in house?.

Nah!! .................... Use candles .. fork handles or four candles even.

NO voltage drop or RCD or TT Earthing, exporting PME or clipped-along-the fence issues then!!