Although this thread has been somewhat of a fail for myself. For what its worth tel, if that was my job i'd be doing option 3 with 3core 2.5 SWA and obviouslly just a bit of 2.5mm t+e from the socket to the fcu.
so what about fusing down for the 2.5mm spur? i am thinking a 13A D/P FCU, but that gives him a very small capacity in the garage.
the 13A is the bugbear though. now the reason for fusung down is that a single 2.5mm requires a lower OCPD than the RFC, as it can only safely carry circa 27A or less id derated. now if a spur was in 4mm, that will carry 32A, so i can see no reason for not installing an unfused spur in 4mm.
though of that, but client will not be pleased to see that behind his LCD TV, which is the only viable place to tap off the RFC. would need to be a isolator and MCB there. unless i fitted them outside in an IP rated enclosure. that's a trhought.
Well look's like im going to have to bite the bullet on this occasion and quite simply eat humble-pie.