hello everyone, I would like to power a shed but the existing electrics in the house are not the best to say the least! C50 breakers old mk sockets and switches etc etc. I can get from the meter to the garden easily enough, then use swa and a board in the shed with a rod etc, but what about the meter end? there is already a dp henly block so I can get a supply before the old cu, would it be ok to fit an rcd by the block to protect the submain, then leave the supply earth at the shed disconnected and make it a tt?
 
Main switch fuse (kmf) after the Henley at the meter > SWA > garage board in shed. Assume wooden shed with nothing to bond?
 
I thought the supply to the shed would need rcd protection- it would be t+e inside the house, adapt box, then swa. so the main house electrics have no bearing on the certificate to be issued?
 
I thought the supply to the shed would need rcd protection- it would be t+e inside the house, adapt box, then swa. so the main house electrics have no bearing on the certificate to be issued?

No what you suggested in the OP.

I don't understand your comment about the cert - sounds like a LABC job to me.
 
Put simply, you don't need to RCD protect an armoured cable, you DO need to RCD protect the sockets on the end of it.

So put a suitably sized fuse / MCB to protect the size of cable you've chosen according to your loading and voltage drop calculations at the upstream end, and an RCD and circuit overload protection at the downstream end. If you've nothing to bond in the shed (so no water/structural steel etc) and the house has TN earthing then just run a 2 core SWA and gland the armour for your earth.
 